Old 11-30-2012, 10:19 PM   #1
Sub panel bonding
Just wondering, with all that I understand about wiring remote panels, mostly 4 wire, what makes it possible that a 3 wire is allowed to have the neutral/ground bonded to case? Under what circumstances is this possible?
marc216 is offline   Reply With Quote
Old 11-30-2012, 10:51 PM   #2
Semi-Pro Electro-Geek
Sub panel bonding
It is no longer code compliant under any circumstances. As the diagram above says, the 2008 NEC removed the use of 3-wire feeds for anything other than a service. 2011 did not change that.
I am a lawyer, but not your lawyer. And who cares anyways? We're here to talk construction. This is DIY advice, not legal advice.
mpoulton is online now   Reply With Quote
The Following User Says Thank You to mpoulton For This Useful Post:
marc216 (11-30-2012)
Old 11-30-2012, 11:44 PM   #3
UAW SKILLED TRADES
Stubbie's Avatar
Sub panel bonding
Well since I'm the author of the drawings I suppose it is prudent that I reply ...
To add to mpoulton 3 wire feeders were the norm to detached buildings for years and are just fine if installed properly. The feeder neutral just did double duty as 'neutral' and 'equipment ground'. The utility only brings 3 wires to your service equipment, the difference is the home owner will never likely fool with those wires.
One issue was other metallic paths existing or being brought to the building at a later date. Bonding neutral to ground allowed neutral current to use these other metallic paths to return to the transformer. Mainly because of improper grounding at the detached structure.
As an example see this drawing
Old 12-01-2012, 12:03 AM   #4
Sub panel bonding
Your drawings are very helpful, great work. So essentially now, 4 wire is the only way providing we dont have EMT, water etc... between the two structures. We still have a separate GES, effective grounding path e.g. steel building, G-rod etc...with the detached structure correct?
What "if" there is an attached metallic element between the two structures e.g. EMT. Then what happens?
Mobile Home Electrical Panel Replacement rrolleston Electrical 2 01-28-2012 06:27 PM
Sub Panel GND and mixed 240/120 VAC branch curiousB Electrical 12 01-17-2012 11:49 AM
Passing wire to another panel theatretch85 Electrical 5 09-21-2009 12:09 AM
Installing new (service?) breaker panel and generator panel Nhrafan Electrical 6 04-01-2008 04:03 PM
turn main panel into a sub panel? tikicarver Electrical 2 01-24-2008 08:37 AM