Sub Panel 275' Away - Electrical - DIY Chatroom Home Improvement Forum
Old 04-09-2012, 03:02 PM   #1
Sub Panel 275' Away
I want to run power to my new shed. The length of the electrical run would be 275' from the main panel in my house. I would like to have a 20 amp circuit for receptacles and a 15 amp circuit for lighting. I realize at this distance voltage drop is going to be a big issue.
What's the best way to do this?
eyajko is offline   Reply With Quote
Old 04-09-2012, 03:33 PM   #2
Julius793's Avatar
the run with pvc #2 copper with a 40A breaker coming into a little sub panel
Electricity will kill you if you give it a chance
Julius793 is offline   Reply With Quote
The Following User Says Thank You to Julius793 For This Useful Post:
eyajko (04-09-2012)
Old 04-09-2012, 03:54 PM   #3
Licensed Electrician
k_buz's Avatar
Rewards Points: 2,006
Just so you know, I just called my supply house and the #2 CU is $1.13/ft.
At 275' x 4 (conductors) = 1100' of wire
Those be some expensive lights and outlets.
If you can, you it might be cheaper to put a separate service on the shed.
Old 04-09-2012, 04:00 PM   #4
Julius793's Avatar
most times its not allowed
Old 04-09-2012, 04:02 PM   #5
k_buz's Avatar
But sometimes you can do it. You would have to contact your POCO to find out for sure...maybe even the AHJ.
The Following User Says Thank You to k_buz For This Useful Post:
plummen (04-09-2012)
Old 04-09-2012, 04:29 PM   #6
Electrical Contractor
rrolleston's Avatar
Rewards Points: 1,012
Send a message via AIM to rrolleston Send a message via Yahoo to rrolleston
Here it's one service per residence.
With Electricity there is the right way to do it and the dead way. Just because it works does not make it safe.
rrolleston is offline   Reply With Quote
Old 04-09-2012, 04:38 PM   #7
k_buz's Avatar
Like I said, you'd have to check with the POCO or AHJ.
I've put services on garages where they installed a 100A welder, barns, pole barns. It really isn't that big of a deal here.
The Following 2 Users Say Thank You to k_buz For This Useful Post:
brric (04-09-2012), plummen (04-09-2012)
Old 04-09-2012, 04:52 PM   #8
A "Handy Husband"
rjniles's Avatar
Rewards Points: 4,252
I would run a MWBC using 6/3 UF and get 2 20 amp circuits. Wire is not going to be cheap. You can draw 13 amps @120 volts on each leg with acceptable voltage drops.
Install a 2 pole GFCI breaker to feed and burial depth only needs to be 12".
Coastal South Carolina
rjniles is offline   Reply With Quote
Old 04-09-2012, 04:52 PM   #9
Rewards Points: 1,548
According to my calculations you can get two allotments of 30 amps at 120 volts using three lengths of #6 copper wire (plus #10 ground) in a 120/240 volt circuit with 3% or less voltage drop.
This will leave reserve capacity to run some tools out there.
When drawing more than half of one of the allotments (more than 15 amps @ 120 volts altogether) you will have to make some effort to balance the load between the two hot wires of the circuit.
Old 04-09-2012, 04:57 PM   #10
Semi-Pro Electro-Geek
Rewards Points: 2,990
That's a VERY expensive breaker, and it's likely to nuisance trip due to capacitive losses in a buried cable that long. A deeper trench would probably be cheaper anyways, if he's already renting a machine.
mpoulton is offline   Reply With Quote
Old 04-09-2012, 04:58 PM   #11
k_buz's Avatar
Depending on the calculations, and what size OCPD is protecting the underground, you would have upsize the GEC.
Old 04-09-2012, 05:35 PM   #12
Licensed Electrical Cont.
Speedy Petey's Avatar
Rewards Points: 1,990
I find that hard to believe.
I have never heard this in NYS.
The Following User Says Thank You to Speedy Petey For This Useful Post:
brric (04-09-2012)
Old 04-09-2012, 07:41 PM   #13
Rewards Points: 1,192
I never worry about voltage drop unless I get a defined constant load. Lights and receptacles? No worry.
bobelectric is offline   Reply With Quote
Old 04-09-2012, 07:51 PM   #14
rrolleston's Avatar
NYSEG would let me keep my old service after I put a 200 amp service on my garage. I wanted to keep it until I had time and money to finish and they would not allow it when I tried. If it's multi family they allow it. If the OP shed is too far away from the road it will end up being really spendy project to get a service to the shed too.
Old 04-09-2012, 07:56 PM   #15
k_buz's Avatar
Curious...how do you know where the OP even is? Power lines could be underground at the back of his lot...right behind his shed.
Panel cleanup gdoucette Electrical 5 06-26-2010 02:01 PM
Sub Panel SoxFan Electrical 2 12-02-2008 10:16 AM
Extending Old Main Circuit Panel lkpowell Electrical 4 10-23-2008 02:15 PM
Installing new (service?) breaker panel and generator panel Nhrafan Electrical 6 04-01-2008 03:03 PM
turn main panel into a sub panel? tikicarver Electrical 2 01-24-2008 07:37 AM