Sub Panel - Electrical - DIY Chatroom Home Improvement Forum
Old 09-30-2012, 06:48 AM   #1
kbc
sub panel
i want a new 100 amp sub panel for an addition i was thinking of running three #1 coppers, a black, red, and white, and a #8 green ground, but i do not know what type of insulation thhn or what, and is 1- 1/4 emt suitable i would run the pipe inside
kbc is offline   Reply With Quote
Old 09-30-2012, 07:52 AM   #2
Licensed Electrician
k_buz's Avatar
Rewards Points: 2,006
How far away is this subpanel? By code, you would only need to run #3's CU to a 100A sub. If you are increasing the wiresize due to voltage drop, you must increase the equipment grounding conductor the same percentage.
1 1/4" will be fine, but if you are pulling a long distance, you may want to upsize to 1 1/2" to make the pull easier. You need a insulation type that is rated for wet locations, THWN is what you should be looking for, however, most THHN you buy is dual rated THHN/THWN.
Old 09-30-2012, 07:52 AM   #3
k_buz's Avatar
If this is a detached structure, don't forget the ground rods.
Old 09-30-2012, 07:56 AM   #4
kbc
i thought #3 copper was rated for 85 amps and it is 60 feet away from main panel
Old 09-30-2012, 07:58 AM   #5
k_buz's Avatar
You thought wrong, at least according the NEC. #3 CU will be fine for your installation.
Old 09-30-2012, 07:59 AM   #6
kbc
isnt #3 rated for 85 amps its 60 feet from main panel
Old 09-30-2012, 08:10 AM   #7
k_buz's Avatar
#3 THHN/THWN is rated for 100A
Old 09-30-2012, 09:02 AM   #8
A "Handy Husband"
rjniles's Avatar
Rewards Points: 4,252
You are confusing the ratings of a NM cable assembly with the ratings for individual THHN/THWN conductors.
Coastal South Carolina
Sub panel to sub panel feeding tvfd27 Electrical 1 08-21-2012 03:01 PM
Section 310.15(B)(6) vs. 210.4. Don't assume, call your friendly AHJs! Daneel Electrical 3 04-11-2012 07:24 AM
Sub Panel SoxFan Electrical 2 12-02-2008 10:16 AM
Installing new (service?) breaker panel and generator panel Nhrafan Electrical 6 04-01-2008 03:03 PM
turn main panel into a sub panel? tikicarver Electrical 2 01-24-2008 07:37 AM