Sub Panel - Electrical - DIY Chatroom Home Improvement Forum
Old 12-01-2011, 03:37 PM   #1
sub panel
i have a 150 amp main panel. i will install a 3 pole 60 amp breaker to feed a 100 amp main lug sub panel.
(1) do i need to run a ground?
(2) there is an empty existing 3/4 flex in the main, can i run 4 #6 thhn in it with a ground if needed?
(3) is there a restriction on how many circuit breakers allowed in the panel because im feeding a 100amp panel with #6 wire?
woofster is offline   Reply With Quote
Old 12-01-2011, 04:33 PM   #2
Electrical Contractor
jbfan's Avatar
Rewards Points: 142
What do you mean 3 pole?
Same building or detacthed.
You need a ground wire.
You need 3 #6 and 1 #10
No restrictions on the number of breakers.
How far does the flex go?
Old 12-01-2011, 06:14 PM   #3
sub panel
thx. sub panel in same bldg. i want to install a 3pole (phase)60 amp breaker in the main panel to supply the 100 amp sub. the main panel is recessed in the wall and hard to get a new conduit in. but there is a spare empty 3/4 flex in the main panel going up to the drop ceiling. can i legally snake in 4 # 6 thhn wires with a ground into it? and is it alright to feed a hundred amp panel with that size wire? need about 14 circuits. 20a or less
Old 12-01-2011, 06:26 PM   #4
Rewards Points: 320
Is this a single phase residential service? You referred to a three pole breaker but three poles is for three phase not usually found in a residential setting. You need a two pole breaker for a single phase panel. The two hot conductors go to the two poles of the breaker. Neutral to the neutral bus, and ground to the ground bus. No bonding of the neutral and ground in the sub panel. I don't have my chart with me but if memory serves me correctly the 3/4 inch flex metal conduit is good for 4 #6 conductors. No problem using the 100 amp panel with a 60 amp service.
teamo is offline   Reply With Quote
Old 12-01-2011, 06:38 PM   #5
yes it is a three phase panel. 3 hots 1 neutral. 4 # 6 and 1 # 8 ground in 3/4 ok?
Old 12-01-2011, 06:40 PM   #6
My 2 cents...make sure you connect that flex to a box if it will not reach the new sub, then install another flex or emt to the sub panel so the wires are not left exposed anywhere
lowvolter is offline   Reply With Quote
Old 12-01-2011, 07:26 PM   #7
still need to know is it legal to pull 4 # 6awg plus a #8 ground (all thhn) in a 3/4 flex.
feeding a 100 amp sub panel with 24 breakers. it will be fused at 60 amps.
Old 12-01-2011, 07:47 PM   #8
Rewards Points: 324
NO.you need a 1"flex..
oleguy74 is offline   Reply With Quote
Old 12-01-2011, 08:13 PM   #9
Licensed Electrical Cont.
Speedy Petey's Avatar
Rewards Points: 1,824
Is this in your home?
Old 12-01-2011, 09:00 PM   #10
this is in a commercial bldg
Old 12-01-2011, 09:40 PM   #11
Sparky
Rewards Points: 510
Then you need to hire an electrician.
Techy is offline   Reply With Quote
The Following User Says Thank You to Techy For This Useful Post:
Speedy Petey (12-01-2011)
Old 12-01-2011, 09:48 PM   #12
Then two things come to mind:
A) If you have to come to a "DIY Home Improvement Forum" to ask this then you obviously have NO place doing this work in a commercial setting.
B) Unless you are a qualified/insured/licensed electrician/contractor you should not be doing this work in a commercial setting. See "A" above.
The Following User Says Thank You to Speedy Petey For This Useful Post:
HouseHelper (12-02-2011)
Panel cleanup gdoucette Electrical 5 06-26-2010 03:01 PM
Sub Panel SoxFan Electrical 2 12-02-2008 11:16 AM
Extending Old Main Circuit Panel lkpowell Electrical 4 10-23-2008 03:15 PM
Installing new (service?) breaker panel and generator panel Nhrafan Electrical 6 04-01-2008 04:03 PM
turn main panel into a sub panel? tikicarver Electrical 2 01-24-2008 08:37 AM