Sub Panel - Electrical - DIY Chatroom Home Improvement Forum
Old 08-07-2011, 08:09 PM   #1
sub panel
I have a 100 amp sub panel in my detached shop putting in a ingound pool with heat pump this requires a 60 amp sub panel can i run another sup panel to the pool or do i need to go into main panel in house thats a 200 amp panel,thanks al.
VINGOEA is offline   Reply With Quote
Old 08-07-2011, 08:30 PM   #2
Missouri Bound's Avatar
Can't you run a 60 amp circuit from either the garage panel or the main panel? Must you have a sub-panel at the pool location? Does the pool require more than just one circuit?
The Following User Says Thank You to Missouri Bound For This Useful Post:
VINGOEA (08-09-2011)
Old 08-07-2011, 08:39 PM   #3
Electrician
SD515's Avatar
Rewards Points: 504
You can, but if you use a lot of power at the shop, I’d consider running it back to the main.
Kyle
The Following User Says Thank You to SD515 For This Useful Post:
Old 08-07-2011, 09:22 PM   #4
Rewards Points: 1,192
Yes you can run a sub panel as long as the total load doesn't exceed the continuise load rules. 80%
bobelectric is offline   Reply With Quote
The Following User Says Thank You to bobelectric For This Useful Post:
Old 08-07-2011, 10:36 PM   #5
Lic Electrical Inspector
electures's Avatar
Rewards Points: 1,108
Now I'm no expert but, I have several concerns. What is the calculated load for the existing subpanel? What size are the existing feeders to the existing subpanel. Is the existing subpanel feed with an insulated ground through conduit the entire run. Does the existing feeder contain a srperate neutral? What is the calculated load for the future subpanel? Does the future subpanel contain motors? Once this information is known it can be determined if you can add the new subpanel to the existing subpanel or if you need to install a net feeder for the pool from the existing service. Feeders are sized at 100% of the calculated load.
All responses based on the 2011 NEC.
If you live in New Jersey click here. All other states click here.
Please check with local, county and state officials as laws may vary.
Sizing motors here. Online motor calculator here. Online calculators here.
electures is offline   Reply With Quote
The Following User Says Thank You to electures For This Useful Post:
Old 08-07-2011, 11:55 PM   #6
" Euro " electrician
frenchelectrican's Avatar
Heat pump for pool ?? that will be pretty good size unit for sure.
Need more specs on this set up.
If that heat pump is 4 tonne or larger it WILL have to be it own circuit the last large heat pump I done on single phase side is 6 tonne that do denfinetly need 60 amp circuit no queston asked.
How much load you have on the house panel ?
The real best answer is do the load caluation so you know how much leeway you have on exsting service.
Merci.
Marc
The Following User Says Thank You to frenchelectrican For This Useful Post:
Old 08-09-2011, 04:56 PM   #7
Sub panel
The sub panel has insulated ground from main panel,i also have driven gd rod for sub panel,right now i'am only using a 5 hp table saw,i thought a 60 amp sub panel would be enough for 220 heat pump and a pool light and some low voltage lighting.
Old 08-09-2011, 06:07 PM   #8
electures's Avatar
Does the subpanel have a seperate neutral conductor (white wire)? Can you post a pic of the subpanel? It will make it easier for us to help you.
Old 08-12-2011, 02:32 PM   #9
YES I ALSO NEED TO WIRE IN A CIRCUIT FOR PUMP FOR FILTER CODE SAYS THIS NEEDS TO BO ON ASEPERATE CIRCUIT SO IAM GOING TO GO WITH SUB PANELTHANKS AL
Old 08-12-2011, 02:36 PM   #10
Looks like iam going to run a sub panel off main panel in house thinking of running sub panel off gfi code says u only need to 12 inches with pvc the only drawback is cost of gfi which way should i go,i will need a 40 amp gfi and 20amp gfi at filter locations if i dont go with gfo in main panel,also does anyone know the code for inground pool light,thanx al.
Old 08-12-2011, 03:19 PM   #11
Master Electrician
Rewards Points: 3,966
The 12" minimum depth in pvc for residences only applies to GFCI protected circuits of 120 volts or less.
brric is online now   Reply With Quote
Panel cleanup gdoucette Electrical 5 06-26-2010 02:01 PM
Sub Panel SoxFan Electrical 2 12-02-2008 10:16 AM
Extending Old Main Circuit Panel lkpowell Electrical 4 10-23-2008 02:15 PM
Installing new (service?) breaker panel and generator panel Nhrafan Electrical 6 04-01-2008 03:03 PM
turn main panel into a sub panel? tikicarver Electrical 2 01-24-2008 07:37 AM