stupid electrical question.
Ok, just curious. In a breaker box, are the neutral and ground bars basically attached? Thanks.
Are they attached? Usually - yes, securely attached to the enclosure.
Are they attached to each other? If you are dealing with a Service Equipment panel, then yes, they are electrically attached to each other. The neutral conductor is intentionally grounded only at the service equipment. The is to ensure a good return path for ground-fault currents to facilitate the proper operation of your circuit breakers. If you are dealing with a sub-panel, they must be kept separated. The neutral is a current-carrying conductor, and as such is isolated from the grounds. The ground is attached -- both electrically and mechanically to the enclosure, and is not considered current-carrying for the proper operation of the branch circuits. |
Thanks. I was curious as my house has a breaker panel (of course!) and then my detached garage has a panel in it as well, fed from the house panel. The wires coming from the house to the garage panel are #2 aluminum for the hot and a #4 aluminum for the neutral. No ground is run from the house to the garage. So at the garage there is a grounding wire run to the grounding rod in the ground.
I was looking inside the panel and was curious as it appears that the neutral and grounding bars are basically attached to eachother. So I was wondering, if they are basically attached to eachother, isn't each one acting like a ground AND a neutral bar since the electricity could flow between them? Hope this made sense....just trying to learn! Thanks. :eek: |
Jamie |
In a subpanel the panel is bonded to the ground bus and the neutral is insulated from the panel and ground. The neutral is usually seperated unless at the service.
Yours is most likely a 3 wire system, which is not allowed today, it was back then. This involved using the conduit as a grounding conductor. And you were/are still required to sink ground rods. |
As Inphase277 has clarified 3 wire feeds to detached buildings are common if no metallic paths other than the feeder existed. For instance a water line to the detached building from the house would require a 4 wire feed. Just recently as of the 2008 code cycle are 4 wire feeds with isolated neutral and ground required for all situations.. There are a lot of jurisdictions still on 2005 or earlier. Pilots installation is perfectly fine under the code cycles prior to adopting 2008 as rgsgww mentioned. In fact you could still install a 3 wire feed if under a code cycle prior to 2008. I just think it would be better to install a 4 wire so you could run water or phone, data lines to the detached garage and it improves human safety.
There is no physical connection between the garage and the house other than the 3 aluminum wires going from the main panel to the garage panel. In other words, no metal pipes for water, etc. Also, so I understand correctly, since there aren't any metal pipes connecting the house to the garage, the 3 wire set up is OK as long as I have a grounding rod (which I do) and the neutral and grounding bars CAN be connected in the subpanel in the garage? However, there is a phone line run to the garage from the house, but I am curious as to how that is tied into the electric? Thanks. |
Edit - Oh I just realized you were asking because of Stubbie's comments. It's because it violates the "no other metallic path" rule. So if you have phone or water or barbed wire or anything metal connecting the structures then you have to use 4 wire. |
| All times are GMT -4. The time now is 05:10 PM. |