Can someone please help me understand what in the world is going on in this pic? 7 cables (all 12/2 Romex) entering a three switch box. The switch in the middle is a 3 way switch. I understand the wiring basics, but this one goes a little beyond me. Also, the triangles represent wire nuts or equivalent.
Much obliged for any light you can shed!
Stephen
srtaylor is offline   Reply With Quote
Old 01-19-2013, 06:16 PM   #2
DIY staff
Rewards Points: 7,174
Post a photo---your drawing is incorrect. (I think)
Old 01-19-2013, 06:25 PM   #3
Pic attached. Rechecking the diagram.
Old 01-19-2013, 06:29 PM   #4
Rewards Points: 6,652
Everything looks fine to me. You have a common Hot, and the Neutrals are all tied together, even though you have two single poles, and a 3-way. So again, what is your question, and are you having some kind of issue with the way it has been hooked up for quit some time?
Old 01-19-2013, 06:29 PM   #5
Better pic
Old 01-19-2013, 06:30 PM   #6
A "Handy Husband"
rjniles's Avatar
Rewards Points: 4,216
I assume dark wire/triangle is black wires and dotted is white.
1 of the 12/2s brings hot and neutral into the box, the hot is pigtailed and looped the the upper terminals of all three switches. All the neutrals are tied together.
2 of the 12/2 feed the switched hot and neutral to a light or other device. The 2 single pole switches in either end of the box.
1 of the 12/2 is the travelers from the 3 way watch to the 3 way at another location.
The last 3 of the 12/2s feed unswiched hot and neutral to switches and/or receptacles at other locations.
Coastal South Carolina
rjniles is offline   Reply With Quote
Old 01-19-2013, 06:37 PM   #7
A "Handy Husband"
rjniles's Avatar
I will add that the 3 way is wired in a noncompliant manner. The cable going to from the 3 way switch to the other 3 way should be a 3 wire cable to include a neutral.
Old 01-19-2013, 06:37 PM   #8
Rewards Points: 240
Something is not right with that 3-way. It doesn't appear to have a neutral.
fa_f3_20 is offline   Reply With Quote
Old 01-19-2013, 06:44 PM   #9
I don't understand how the three way switch in the middle works...I thought I needed. 12/3.
What would it take to make it compliant?
Old 01-19-2013, 06:56 PM   #10
Go back and look again. That white on the lower left is the Neutral/Common. It is just that the Travelers are both black. There is no ground showing though, that would be a problem with today's standards if they make any changes to the circuits.
Old 01-19-2013, 07:06 PM   #11
A "Handy Husband"
rjniles's Avatar
re the 3 way. They are using the black and white of a 12/2 as trsvelers and picking up a neutral at the far end. Not kosher.
Old 01-19-2013, 07:11 PM   #12
Resi EC
Rewards Points: 252
Looks okay to me.
Probably a two wire feed and traveler, switch leg is at the other switch.
So both switches have neutrals, but as old as that work looks, neutrals would not have been needed, code compliant when built.
Use to be quite common.
Gac66610 is offline   Reply With Quote
Old 01-19-2013, 07:17 PM   #13
Helpful comments. Thank you, everyone. I would like to turn the switch on the right into a 3-way switch. Easy enough for me to replace the furthest right romex with 12/3 for running it to the rest of that circuit. Technically, does messing with that switch mean I need to rewire anything else?
Old 01-19-2013, 09:04 PM   #14
joed's Avatar
Rewards Points: 12,950
To make the right switch a three way is simple once you get the cable to the new switch. You need a 12/3 cable to the new switch.
I am going to skip ground wires in the description. Connect all of them together and to the switch if it has a ground screw.
Remove the two black wires from the existing switch. Leave everything else alone.
Connect one black wire to the common screw of your new three way switch#1.
Connect the other black wire to the black wire to your new switch#2 cable.
Connect the red and white wires to the remaining two traveller screws of the new switch#1.
At new switch#2 connect the black to the common screw.
Connect the red and white wires to the remaining two traveller screws of the new switch#2.
The Following User Says Thank You to joed For This Useful Post:
srtaylor (01-19-2013)
Old 01-19-2013, 09:29 PM   #15
Originally Posted by joed
To make the right switch a three way is simple once you get the cable to the new switch. You need a 12/3 cable to the new switch..
I assume 14/3 is also an option?
Tags
electrical switch , romex
Question on wiring two banks of lights from two switches dustycreek Electrical 3 09-09-2012 04:34 PM
Wiring switches in Ontario demandrew Electrical 4 12-14-2011 09:30 PM
Wiring multiple outlets, switches and lights Bubski27 General DIY Discussions 3 11-09-2011 06:54 AM
Question about wiring and voltage with switches and lights rswurth Electrical 17 06-20-2010 11:12 PM
strange wiring everyman Electrical 10 07-06-2009 08:38 PM