-   -   Strange problem w. wall outlet, please help! (http://www.diychatroom.com/f18/strange-problem-w-wall-outlet-please-help-23936/)
yiplong 07-19-2008 09:25 PM
I have a wall outlet on 40 amp circuit, intended for use w. AC units. It currently supplies power but seems a bit unstaple. When I plugged the AC in, the air that it pumped out was not cold, and the fan seemed to be revving up and down. When the same AC is plugged into a 15 amp circuit, it operates normally, but will kick the breaker.
When I plugged a power strip into the 40 amp outlet, it instantly burnt the power strip.
Has anyone faced this problem before? What is going on here?
yiplong 07-19-2008 09:44 PM
I should clarify that the AC is 115V, 15 amp. The receptacle it is plugged into is on its own 40 amp circuit.
Stubbie 07-19-2008 10:07 PM
What voltage at the outlet? And why do you say 40 amps? Are you sure your not connecting to a 240 volt branch circuit.
Termite 07-19-2008 10:59 PM
I'm picturing a standard 15 or 20 amp duplex-type receptacle for some reason, although I hope I'm wrong. What sort of receptacle is this? Can you post a picture?
BigJimmy 07-19-2008 11:03 PM
Hey, guys. I was very reluctant to reply as this seemed beyond bizarre.
Jimmy
Termite 07-19-2008 11:11 PM
Bizarre tends to get my curiosity going....:huh:
yiplong 07-19-2008 11:54 PM
Hey all, thanks for the replies. I'm not sure what voltage is at the outlet itself, I can check when I get a multimeter tomorrow.
The receptacle has only one outlet, the ground is hemespheric, one of the other two holes looks like a T turned on its sides, the other one looks just like an I. I can post a picture of it tomorrow.
I should add that the AC, after running for a while (w/o producing any cold air) would kind of turns itself off, sometimes completely off, other times it just makes noise and won't even pump out any air.
Thanks for any input.
fw2007 07-20-2008 07:14 AM
I am going to assume a few things:
Judging by the fact that you are able to plug the AC into a standard 120V 15A outlet, it has a standard plug, and operates on 120V.
Next; Since you were able to plug the power strip into the 40A outlet, I assume that this outlet is a single, standard 120V type as well.
Finally, since the power strip burned out, you must have 240V at the 40A outlet.
What does the 40A breaker look like? Is it much thicker, and does it have two handles that are bonded together?
If you do have 240V at the 40A outlet, you must either change the circuit to 120V, or change the outlet to a 240V type.
In any case, I strongly recommend that you get an electrician to evaluate your situation.
FW
fw2007 07-20-2008 07:19 AM
One more thing:
What is the size of the AC unit? If you can read the BTU, voltage, and ampere rating on the panel (can be located on the side of the AC or inside where the filter is), that would give everyone here a better idea of what you are dealing with.
FW
ccarlisle 07-20-2008 08:02 AM
1 Attachment(s)
Is this what you have at the wall? I think that's a 240V 20Amp plug...
BigJimmy 07-20-2008 10:09 AM
Looks like he had a rough night at the tavern!
yiplong 07-21-2008 03:51 PM
No, the outlet looks like this:
http://www.homefurnish.com/CMS400Min...7Small_175.jpg
The one depicted in the picture has two outlet, mine has only 1, but they are the same design.
The AC is 9000 BTU, 15 amp, 115V.
The breakers are two 20 amps breakers, which make the circuit 40 amp.
jerryh3 07-21-2008 05:08 PM
I see this going downhill very fast.
Stubbie 07-21-2008 05:21 PM
And you have revealed your problem. You have a 240 volt branch circuit wired to a 120 volt receptacle configuration. Pretty stupid but I've seen this done before.The 20 amp double pole breaker is not 40 amps.... you don't add them together. What you have is a 240 volt 20 amp branch circuit. The good news is you can reconfigure this for your outlet and operate your ac as long as you haven't damaged it yet with the overvoltage. You will need someone to open the panel box and change the wiring connections and I would likely change the breaker to a 20 amp single pole (about 4 bucks).
If you don't want an electrician at this point we can tell you what to do, however if you are the least bit uncomfortable doing this I'd opt for the electrician.
Pudge565 07-21-2008 07:34 PM
Not nessecrely stubbie he could have a multiwire branch circuit. Although unlikley it is possible but it does sound like he has 240 going to it and not 120.