Strange Issue With Sub Panel Installation - Electrical - Page 2 - DIY Chatroom Home Improvement Forum
Old 06-06-2014, 04:58 PM   #16
Licensed electrician
Rewards Points: 1,772
Is the original panel a GE?
Old 06-06-2014, 05:12 PM   #17
Licensed Pro
Check your cable clamps... too tight can cause a short.
Old 06-06-2014, 05:22 PM   #18
Rewards Points: 3,396
Looks like Square D.
Curious, where you going with it if it was GE ?
ritelec is offline   Reply With Quote
Old 06-06-2014, 05:27 PM   #19
I'm thinking the op found the issue.
Old 06-06-2014, 07:08 PM   #20
Rewards Points: 1,832
Originally Posted by ritelec View Post
Interesting.
Sounds like that circ is back fed and as you close the connection at the breaker it trips the two pole feeder breaker.
That it also didn't trip in the main panel because it was possibly on the same legg.
You would have done it live, but you wired it and didn't get rapped, .
with that breaker off.
check to see if that circuits hot?
My best guess would be a short on that circuit plus a defective branch breaker.
Replace the branch breaker with another and see what happens. If that breaker trips its a short.
Jump-start is offline   Reply With Quote
Old 06-06-2014, 07:24 PM   #21
dmxtothemax's Avatar
Rewards Points: 5,506
Originally Posted by mrules45 View Post
I had to move one 20 amp tandem and another 20 amp single pole breaker to get space. 3 circuits total.
1 - What loads are on these circuits that you have moved ?
2 - Did they work ok before the shift ?
3 - Can you turn off these breakers, and tell us what voltage is on the line side of these breakers,
A - measure reletive to neutral.
B - On the tandem measure between the two hots, as well as reletive to neutral.
Post your results.
4- Measure also on the load side for voltage.
You will need a volt meter for these measurements
Also are you confident you can do this safely ?
dmxtothemax is online now   Reply With Quote
Old 06-06-2014, 09:02 PM   #22
Electrical Contractor
jbfan's Avatar
Rewards Points: 552
Originally Posted by Robpo View Post
If the tandem breaker is the same brand as the other breakers(it looks like it might be different) I would shut off the 50 amp and turn all the others on and then turn the 50 on and see if one of the other breakers trip. I can't see anything wrong.
Not a smart way to trouble shoot.
Old 06-16-2014, 10:47 AM   #23
Rewards Points: 18
My guess - in the original panel, the two circuits on the tandem were on the same phase (because that's how a single tandem works). On the other end, they are shorted together. That would appear to work fine, even though the neutral could be overloaded. When you moved them over to the sub, you put them on opposite phases, and thus they would trip the 50A breaker.
The fix is to find out where they are shorted and fix it there. It may be a split receptacle where someone forgot to break the tab...
/mike
n1ist is offline   Reply With Quote
Old 06-16-2014, 05:20 PM   #24
The big thing here is that a 50amp breaker is tripping before a 20 in series. Something is very wrong. Either 2 circuits on the same leg are faulting simultaneously or the tandem is defective. Yes I know it could be that by chance the 50amp might have a faster magnetic trip curve over the 20, but still Id replace it just in case. After the short is found of course.
Old 06-16-2014, 05:24 PM   #25
Not unknown or wrong !
It's a thing known by many experienced electricians.
It's simply because there is more current available at the 50A breaker
because there's less things in the way to impedeed the current flow !
Old 06-16-2014, 07:01 PM   #26
Assuming minimal loads and none of the loads pull substantially more current under a voltage sag 4000amps of fault current (assuming) on the tandem will also be seen at the 50amp breaker. The big breaker doesn't see more fault current. Impedance values are summed.
Electricians may see large breakers blow first but its more from either the natural variance in trip curves (very much the norm on breakers from different makers) on molded case breakers or the branch is defective.
Mobile Home Electrical Panel Replacement rrolleston Electrical 2 01-28-2012 05:27 PM
Sub Panel GND and mixed 240/120 VAC branch curiousB Electrical 12 01-17-2012 10:49 AM
Passing wire to another panel theatretch85 Electrical 5 09-20-2009 11:09 PM
Replacing 2 Sub Panels with 1 Larger Panel GuitarJack Electrical 7 08-25-2009 08:43 PM
Multiple Sub Panel Installation Handyman2007 Electrical 26 12-31-2007 05:47 PM