Old 08-24-2012, 03:31 PM   #16
Rewards Points: 1,062
Originally Posted by jbfan View Post
Thats only rated for 70 amps!
OK, i understand that would apply for the neutral. however, thinking alongside the logic that allows for the ground to be thinner than the rest of the wires rated for a certain amperage, can i use a lug rated for 70A for the ground in a circuit rated for 100A?
in other words, if the ground wire in this cable is AWG 6 and the rest are 2 and if that ground had insulation and you used it for hot or neutral you could go up to 60A or so, i believe, can you also apply the same discount to the lug?
i am just trying to think logically here
Old 08-24-2012, 04:32 PM   #17
Lic Electrical Inspector
electures's Avatar
Rewards Points: 1,108
As long as the calculated load on the neutral doesn't exceed 90A. And since #2 SER cable has #2-#2-#2 and #4 awg conductors, a #2 AL grounded conductor is rated for 90A. The lug should be fine.
All responses based on the 2011 NEC.
If you live in New Jersey click here. All other states click here.
Please check with local, county and state officials as laws may vary.
Sizing motors here. Online motor calculator here. Online calculators here.
electures is offline   Reply With Quote
Old 08-24-2012, 04:38 PM   #18
It is the GROUND i am referring to. Not the neutral. The rated amperage for the neutral is the same as for the hots, as the wire is the same thickness also. But the ground wire is thinner, hence my idea of using a smaller lug too (but how much smaller, i.e. is 70A rating going too much?)
Old 08-24-2012, 06:00 PM   #19
electures's Avatar
The terminal is listed for certain wire sizes. Since it is a ground wire the ampacity of the terminal is irrelevant.
Wire Gauge and Circuit Breakers Red Truck Electrical 21 01-21-2012 06:33 AM
What size ground wire should I use for 8 gauge power dxmullin Electrical 1 07-06-2011 02:57 PM
Wire Gauge for 30A RV Outlet (long span) jayne1986 Electrical 24 02-20-2011 08:18 PM
My 12 gauge wire fiasco, overkill needing removal ChrisDIY Electrical 8 01-25-2011 06:47 PM
connecting straight wire to stranded Cossack Electrical 5 07-30-2010 01:52 PM