Stranded Vrs Solid Copper Wire - Electrical - Page 2 - DIY Chatroom Home Improvement Forum
Old 05-06-2013, 11:33 AM   #16
Special User
Rewards Points: 1,230
According to http://www.electrician2.com/calculat...cpd_ver_1.html a 26A load wants 8ga wire on a 40A breaker and will have a 1.2% voltage drop out of an allowed 5% at 70ft.
For wires I will be curling around screw terminals I prefer solid. For everything else, stranded is the way to go IMHO.
The above post is for entertainment purposes only. Its contents may, and probably will, lead to legal liability and damage or loss of property, life, or limb. Use at your own risk.
tylernt is offline   Reply With Quote
Old 05-06-2013, 01:35 PM   #17
Originally Posted by electures View Post
Fused or non fused disco?
non-fused disconnect.
rcassidy is offline   Reply With Quote
Old 05-06-2013, 11:24 PM   #18
" Euro " electrician
frenchelectrican's Avatar
Originally Posted by rcassidy View Post
The AC unit name plate data states 240 V, MCA= 26A, MOP= 45A. The AC unit will be approximately 70 ft from the main distribution panel. Not sure I fully understand NEC Table 310.16 regarding wire size.
What size wire should i use and what size breaker?
#10 copper THHN ( NM cable < 10-2 #> are ok with this distance ) with 40 amp breaker.
There is a special rules we can use due the A/C compressour it being used so it will use Art 430 et Art 440* there is some extempt with sizing on the conductors.
Merci,
Marc
* Only in NEC codes 2005 , 2008 and 2011 NEC editons are the same.
# SVP remark the white conductor to other colours so that way someone else do not make a mistake as neutal due this will be used as line conductor not netural
Old 05-07-2013, 02:14 AM   #19
Electrical Contractor
kbsparky's Avatar
We would use a #10 wire with a 45 Amp breaker for such an installation.
And, yes, we do have 45 Amp breakers on hand for these types of jobs.
-KB
Old 05-07-2013, 02:52 AM   #20
Rewards Points: 1,192
Never saw a device over 20 amps that didn't have pressure connections.
bobelectric is offline   Reply With Quote
Old 05-07-2013, 06:35 AM   #21
Rewards Points: 150
if you are going through the attic you may need to make an adjustment for ambient temp see derating table
usair is offline   Reply With Quote
The Following User Says Thank You to usair For This Useful Post:
mm11 (05-07-2013)
Old 05-07-2013, 09:29 AM   #22
Special User
Purely for my own education, what temperature does one consider an attic to be? I've never seen this in the NEC... there are some ASHRAE "suggestions" of 140F but I don't know if the NEC accepts ASHRAE for code purposes.
Old 05-07-2013, 12:18 PM   #23
Originally Posted by frenchelectrican View Post
However this part it may get ya in a small bind due 45 amp breaker is not a super common item but they do have it if you order it otherwise 40 amp is most common size breaker and IMO it should hold allright but before you go get the 40 amp breaker SVP post the minuim running amps first before we will suggest the correct breaker size.
Merci,
Marc
I wrote the underline part and I know KBsparky did mention 45 amp breaker which I can get it in state side and most big box store may not stock this size but can be ordered or go to electrical supply centre to order that one.
What brand name breaker you have there?
Merci,
Marc
Old 05-07-2013, 12:22 PM   #24
Not really in most case. you will have to use the common sense depending on where ya located and the type of attic it being used and the tempture will bounce anywhere from 48C to 62C ( 120 to 145F ) but if any conductors being run on the rooftop that will compound it may go higher than attic tempture all it depending on the set up.
Merci,
Marc
Alarm Wire, Stranded or Solid? gfchew Electrical 7 04-11-2016 03:04 PM
Connecting Copper Wire to Aluminum Wire StarStryker11 Electrical 3 12-21-2012 12:48 PM
Use red and black wire as 110 in Canada mattm Electrical 10 11-26-2012 07:40 PM
How To Solder Copper Pipes Termite How To Guides 69 11-13-2012 12:20 PM
Neutral Wire? 4x15mph Electrical 8 11-24-2008 01:00 PM
