stranded vrs solid copper wire
I'm in the process of installing central AC (4 ton). I plan to install #8 wire from the panel to the AC disconnect switch. Shall I use stranded or solid copper #8 wire?
thank you
rcassidy is offline   Reply With Quote
Old 05-05-2013, 07:11 PM   #2
Electrician
Rewards Points: 792
They don't make solid #8(at least I have never seen it) so you will have to use stranded.
darren is offline   Reply With Quote
Old 05-05-2013, 07:17 PM   #3
Electrical Contractor
kbsparky's Avatar
What does the nameplate on the unit say?
Minimum circuit amps:
Maximum overcurrent protection:
-KB
Old 05-05-2013, 07:19 PM   #4
Lic Electrical Inspector
electures's Avatar
Rewards Points: 1,108
#8 and larger installed in a raceway shall be stranded.
All responses based on the 2011 NEC.
If you live in New Jersey click here. All other states click here.
Please check with local, county and state officials as laws may vary.
Sizing motors here. Online motor calculator here. Online calculators here.
electures is offline   Reply With Quote
The Following 2 Users Say Thank You to electures For This Useful Post:
ddawg16 (05-05-2013), micromind (05-05-2013)
Old 05-05-2013, 07:20 PM   #5
Max overcurrent protection is 45 amps.
Old 05-05-2013, 07:23 PM   #6
electures's Avatar
What is minimum circuit ampacity?
Old 05-05-2013, 08:49 PM   #7
JOATMON
ddawg16's Avatar
Rewards Points: 1,458
You can get bare copper down to about #4...
ddawg16 is online now   Reply With Quote
Old 05-05-2013, 08:57 PM   #8
Electrician
Rewards Points: 792
I have seen 2/0 bare, but the OP was asking about solid vs stranded.
Old 05-05-2013, 08:58 PM   #9
electures's Avatar
They make #2 AL solid
Old 05-05-2013, 09:02 PM   #10
Licensed electrician
Rewards Points: 1,502
It really doesn't help the OP regarding the availability of larger bare conductors. They need insulated for their install.
Old 05-05-2013, 09:07 PM   #11
Licensed Electrician
k_buz's Avatar
Rewards Points: 2,006
Use stranded. At the either 10 or 8 gauge, it will be the most readily available and easiest to work with.
Old 05-05-2013, 09:46 PM   #12
" Euro " electrician
frenchelectrican's Avatar
thank you
I will make it very simple .,
They are only come in stranded once you get #8 or larger ( I know you can get them in soild but IMO that not even worth the hassle with it.)
As few other members asked what is the minuim running amps and I know you did posted the max running amp which you stated 45 amp.
Look at the name plate again and look for minuim size and this how we will sized the conductors from that sized conductor on minuim and breaker on max running amps.
However this part it may get ya in a small bind due 45 amp breaker is not a super common item but they do have it if you order it otherwise 40 amp is most common size breaker and IMO it should hold allright but before you go get the 40 amp breaker SVP post the minuim running amps first before we will suggest the correct breaker size.
Merci,
Marc
The Following User Says Thank You to frenchelectrican For This Useful Post:
MTN REMODEL LLC (05-06-2013)
Old 05-06-2013, 09:34 AM   #13
The AC unit name plate data states 240 V, MCA= 26A, MOP= 45A. The AC unit will be approximately 70 ft from the main distribution panel. Not sure I fully understand NEC Table 310.16 regarding wire size.
What size wire should i use and what size breaker?
Old 05-06-2013, 10:37 AM   #14
electures's Avatar
Fused or non fused disco?
Old 05-06-2013, 11:01 AM   #15
#10 copper wire and a 40 amp breaker.
The Following 3 Users Say Thank You to Jim Port For This Useful Post:
frenchelectrican (05-06-2013), jbfan (05-06-2013), stickboy1375 (05-07-2013)
Alarm Wire, Stranded or Solid? gfchew Electrical 7 04-11-2016 03:04 PM
Connecting Copper Wire to Aluminum Wire StarStryker11 Electrical 3 12-21-2012 12:48 PM
Use red and black wire as 110 in Canada mattm Electrical 10 11-26-2012 07:40 PM
How To Solder Copper Pipes Termite How To Guides 69 11-13-2012 12:20 PM
Neutral Wire? 4x15mph Electrical 8 11-24-2008 01:00 PM