Stove Top And Under Counter Oven On Same Wire - Electrical - DIY Chatroom Home Improvement Forum
Old 03-19-2014, 07:26 AM   #1
stove top and under counter oven on same wire
I am changing out my free standing stove/oven to a counter top stove and under counter oven. I have a current 50 amp breaker in my breaker box for the freestanding unit. The cooktop calls for 30 amp and the oven calls for 20 amp. I don't yet know the current wire size I have, but can I run both new units through the current wire back to the breaker?
mtbjs is offline   Reply With Quote
Old 03-19-2014, 07:40 AM   #2
I am
Yes... but you would have to feed the top and oven with the 30 and 20...
Install a small sub panel ... feed in with the 50, and take the two circuits from it.
(note: your current 50 amp may be 3 wire... new codes require a 4 wire, if 4 wire you should be good to go. If 3 wire you "may" want to run the two circuits back to the main (or other 4 wire sub ) panel...
UnclePhil is offline   Reply With Quote
Old 03-19-2014, 08:10 AM   #3
So if I have a sub panel, can it be in the new cabinet I ordered for the stove and oven, so that I have only one plug on my wall?
Old 03-19-2014, 08:24 AM   #4
A "Handy Husband"
rjniles's Avatar
Rewards Points: 4,192
A sub panel would have to meet the working space requirement in front of the panel. Located in a cabinet would not do it. Run a new 20 amp circuit. If the old circuit is 3 wire, rerun that also.
Coastal South Carolina
Old 03-19-2014, 09:14 AM   #5
Licensed Pro
If the existing 50A circuit is fed with 6/3 Cu, you can feed both cooktop and oven from that circuit using a junction box, no subpanel required.
The Following 2 Users Say Thank You to HouseHelper For This Useful Post:
brric (03-19-2014), Stubbie (03-19-2014)
Old 03-19-2014, 09:20 AM   #6
So does that mean I end up with two plug ins on the wall behind the oven? In other words can I somehow wire the stove and oven up to one cord to plug in to the existing receptacle ?
Old 03-19-2014, 09:23 AM   #7
Licensed Pro
Both should be hard wired in, no plugs.
brric (03-19-2014), UnclePhil (03-19-2014)
Old 03-19-2014, 09:27 AM   #8
I am
not sure what you mean by one plug , but yes, you can put the panel in the cabinet...
There are clearances and working space around panels and electrical equipment in general as per code..
As suggested you can run new circs back to your panel if you want..
It doesn't necessarily mean that those clearances where observed there...but..
Old 03-19-2014, 09:31 AM   #9
I am
There are a few "tap rules" around... but none that I've seen that say you can splice these two loads (one-20amp, one-30amp) on a 60 amp circuit...
There's something about protecting the wire where it receives it power....
enlighten me please..
Thank you
Old 03-19-2014, 10:04 AM   #10
Master Electrician
Rewards Points: 3,826
Thank you
2011 NEC 210.19(A)(3) and 210.19(A)(4).
brric is offline   Reply With Quote
Old 03-19-2014, 10:08 AM   #11
Master Electrician
Post make and model numbers of the appliances and/or spec sheets. Also need to know the size and number of conductors of the existing branch circuit.
Old 03-19-2014, 10:22 AM   #12
I am
Thank you.
Old 03-19-2014, 10:33 AM   #13
Stove top and oven both Frigidaire. Stove top is 30" 4 burner model # FFEC3024LB, which its spec sheet says
Amps @ 240 Volts: 30.8 / 26.9
Connected Load (kW Rating) @ 240V: 7.4 / 5.6
Minimum Circuit Required (Amps): 30A
Power Supply Connection Location: Right Rear
Voltage Rating: 240V / 208V, 60Hz
Oven is 30" model # FFEW3025PS, Which spec sheet says
Amps @ 240 Volts: 15.4 / 13.5
Connected Load (kW Rating) @ 240V: 3.7 / 2.8
Minimum Circuit Required (Amps): 20A
Power Supply Connection Location: Left Rear Bottom
If your question on size and number of conductors for branch circuit means the wire to the existing oven, I plan to run new wire from the breaker box to the stove/oven since it needs slightly longer run
Old 03-19-2014, 12:56 PM   #14
Master Electrician
If the appliances are adjacent to one another you could run 6-3 w/g to a large jbox, probably located under the cooktop. Then go to the jbox with the provided flexible metallic conduit from each appliance.
IMO if your not too proficient to this I would suggest separate feeds. 10-3 w/g to the cooktop and 12-3 w/g to the oven. The spec sheets show suggested locations for the jboxes to which you would run the feeders and the splice the conductors from the feeders to the metallic whips of the appliances.