Is Stapling Cable To Beams/studs A Code Req ? - Electrical - DIY Chatroom Home Improvement Forum
Old 07-02-2008, 10:56 AM   #1
Rewards Points: 1,062
Question
is stapling cable to beams/studs a code req ?
or just an option left to those neat-minded. if so, how frequently do they have to be set (like every foot or so) ?
Old 07-02-2008, 11:40 AM   #2
Registered User
Termite's Avatar
Yes, wires have to be secured. You're supposed to secure within 12" of a fixture as I recall, and every 4-1/2' of run. Honestly, if it is secured I never hassle someone, and I'd never consider taking a tape measure to the staple spacing unless they're really leaving out staples.
Old 07-02-2008, 12:18 PM   #3
Rewards Points: 82
If you are fishing the wires into an existing wall, or ceiling that has no access no staples are required.
Old 07-02-2008, 12:27 PM   #4
Licensed Pro
And it is within 8" of a single gang plastic box.
Old 07-02-2008, 04:47 PM   #5
Registered User
Termite's Avatar
The 8" requirement is an exception to the 12" rule for when a box without any kind of cable clamp is used. (IRC table E3702.1, footnote H) Some plastic boxes have integral "clamps", some do not.
Like I said, if the inspector is hassleing you on this, he's looking for things because he's a jerk, or you're really left some major staples out...Or he's PO'd at you for something! I have called it, but only when a builder wants to dispute everything with me. I tend to be more "thorough" when someone's being unprofessional!
Old 07-02-2008, 09:24 PM   #6
Electrician's Helper
Pudge565's Avatar
Rewards Points: 150
Send a message via AIM to Pudge565
I thought that it was within 6" of a box.
Pudge565 is offline   Reply With Quote
Old 07-02-2008, 11:40 PM   #7
Registered User
Termite's Avatar
Nope.
Old 07-03-2008, 12:12 AM   #8
liscenced electrician
Rewards Points: 538
as a standard ive always done within 6" of every box and every 4 feet to allow some wiggle room. but the code says:
334.30 Nonmetallic-sheathed cable shall be supported and secured by staples, cable ties, straps, hangers, or similar fittings designed and installed so as not to damage the cable, at intervals no exceeding 4 1/2 feet and within 12 in of every outlet box, junction box, cabinet, or fitting.
334.30(A) basically holes in wood count as being supported
334.30(B)(1)You don't have to support the cable if its fished in a wall
(2)you don't have to support within 12" of equipment of light fixtures or equipment if the connection is accessible
Do yourself a favor and run all your wires with 90 degree angles, don't make your attic look like a spiderweb, run everything together from the panel and then make hard turns from there
jimmy21 is offline   Reply With Quote
Old 07-03-2008, 12:57 AM   #9
Hi, i'm new to this forum and need some advice. We have a new hollow wall (no studs) system where the wiring is secured and clamped at the top of the wall and is loose in the wall to the switches and outlets where a clip (not the boxes) secures the wire into the electrical box. The walls are thick enough to protect the wire. Question, can this be considered to code? Or can this be approved by whom? We have been getting a wide range of options even from City inspectors, probably due the unique design.
Thanks!
macwall is offline   Reply With Quote
Old 07-03-2008, 01:12 AM   #10
Rewards Points: 538
for a new installation. no that would not be code at all. Who knows if it was legal when it was installed. Id leave it alone though. if it aint broken, don't fix it
Old 07-03-2008, 09:02 AM   #11
Registered User
Termite's Avatar
Thanks!
Is the wiring and/or the wall system new? If so, I'd require that the wire be supported per code by an approved method. That's the problem with some of these new basement finishing panel systems.
I'd suggest contacting your wall system's manufacturer to see how the product's listing suggests dealing with this code issue.
Old 07-03-2008, 09:42 AM   #12
Licensed electrician
Rewards Points: 1,284
Does this system just have built-in chases for the wiring to be run in?
Perhaps the inspector would consider this the same as fishing a cable where it is not required to be secured.
underground code tom b Electrical 8 03-23-2008 11:55 AM
code for underground service tom b Electrical 6 10-10-2007 12:48 PM
Coaxial Cable Question bahaisamurai Home Theater 9 08-08-2007 03:54 PM
Another Bryant 383KVA with code 31 problems rpgIVguru HVAC 1 02-05-2007 02:47 PM
1950's Roof Framing Strength KempLN Building & Construction 21 06-17-2006 11:06 AM