Old 07-16-2012, 11:44 AM   #1
Square D Homelite Main Panel - Ground / Neutral Bonding
This is a 200 amp main panel which will feed a 200 amp sub panel back to back. From the way things look on this panel it looks to be bonded already. No green bonding screw to be found inside. See attached pictures. It looks like the neutral coming in from the power company ties into a bar and then there is a place for my ground and neutral to tie in the top left part of the panel on my side (two lugs with one being bigger than the smaller one). I believe at this point it is bonded with the panel. Its a clean way to do it if my thinking is correct or maybe im wrong.......thats why im here asking questions.! Help!
P.S. The current Main panel is out in the yard on a small telephone pole so im shifting it over beside the house (Back to back with inside subpanel) and going from aerial to underground service.
Square D Homelite Main Panel - Ground / Neutral Bonding-summerville-20120713-00935.jpg   Square D Homelite Main Panel - Ground / Neutral Bonding-summerville-20120713-00937.jpg   Square D Homelite Main Panel - Ground / Neutral Bonding-summerville-20120713-00936.jpg
erm1981 is offline   Reply With Quote
Old 07-16-2012, 12:23 PM   #2
UAW SKILLED TRADES
Stubbie's Avatar
Your correct. What you have is called combination metering equipment and is rated 'service equipment only'. In other words neutral and ground will be permanently bonded since this will be the location of the main disconnecting means and utility meter in one enclosure.
Your going to be feeding your other panel via the feed thru lugs shown at the bottom of the panel busses and will be utilizing a 4 wire H-H-N-Grd feeder with neutral and ground separated at the panel after the service equipment panel.
Old 07-16-2012, 03:30 PM   #3
Licensed Electrician
jrclen's Avatar
Where are the load side meter stabs?
John
jrclen is offline   Reply With Quote
The Following 3 Users Say Thank You to jrclen For This Useful Post:
brric (07-16-2012), frenchelectrican (07-17-2012), Speedy Petey (07-16-2012)
Old 07-16-2012, 03:40 PM   #4
Electrical Contractor
Good catch!
Yes I am a Pirate, 200 years too late. "Jimmy Buffett"
Old 07-16-2012, 04:13 PM   #5
kbsparky's Avatar
No bonding screw is needed, as others have pointed out the neutral is permanently bonded. Also:
1) The inside cover that separates the utility wires from the rest of the enclosure is not in the proper position.
2) The load lugs of the meter socket are missing. Where did you buy this from?
-KB
Old 07-16-2012, 04:28 PM   #6
Licensed Electrical Cont.
Speedy Petey's Avatar
You saw that too, huh?
Old 07-16-2012, 05:11 PM   #7
jrclen's Avatar
Yeah I did. I'd hate for the OP to call the power company for connection and have them catch it.
John
Old 07-16-2012, 05:32 PM   #8
E2 Electrician
stickboy1375's Avatar
You are missing PVC bushings on your terminal adapters as well....
Old 07-16-2012, 05:44 PM   #9
Not required, but I use them also.
Old 07-16-2012, 05:47 PM   #10
E2 Electrician
Im going with required. Also, if you read 352.46, Im still going with required even with wire size #4 or smaller.
Old 07-16-2012, 05:50 PM   #11
Damn it. You need to stop catching me on theses.
Was this a change within the last couple of code cycles?
Old 07-16-2012, 05:51 PM   #12
E2 Electrician
Im on the 2005 in Connecticut. That's the NEC I have in front of me.
Old 07-16-2012, 05:51 PM   #13
Nope.
Old 07-16-2012, 05:54 PM   #14
E2 Electrician
Nope.
No worries...
Old 07-17-2012, 12:46 AM   #15
Since the sub panel is so close does a seperate ground need to feed it? It currently has one running to it but im wondering if that is needed anymore since im grounding the main service panel and its pretty much back to back with
50 Amps for a garage help IcyShadowz Electrical 48 05-31-2012 11:58 PM
Main Electric Panel Help Redrum Ninja Electrical 13 10-22-2011 08:28 PM
Ground and Neutral in Panel bvbellomo Electrical 21 07-17-2010 10:53 AM
sub panel ground and neutral daddyrabbit Electrical 3 01-29-2010 07:49 AM