Square D 150 Amp Homelite Panel Question - Electrical - DIY Chatroom Home Improvement Forum
Old 04-13-2009, 05:33 PM   #1
RustyRealtor's Avatar
Rewards Points: 287
Hello,
Trying to save some money, I replaced my old Fed Pacific breaker box with the above mentioned Square D box. It seemed so simple when I started and the more I read, the more confused I become. I am going to hire an electrician to look at it and make sure it is alright.
Here is my question: I put the two stranded aluminum hot wires from the meter into the two respective lugs and tightened them with an hex wrench. In the center of the two hot lugs is another hex lug with a large 'N' underneath it. I placed the neutral from the meter into this lug. Is this correct? If so, then what is this LK100AN neutral terminal kit which came with the box?
Many Thanks,
Russell
RustyRealtor is offline   Reply With Quote
Old 04-13-2009, 06:42 PM   #2
http://ecatalog.squared.com/techlib/...0089268021d6e1
From the instruction card, it look to be a means to attach large wire (#6-2/00) to the neutral busbar.
surrogate is offline   Reply With Quote
Old 04-13-2009, 07:01 PM   #3
Rewards Points: 287
Thanks for the reply.
I guess I don't understand what the large center lug with the 'N' under it is for? I will take some picture and post them tomorrow.
Thanks,
Russell
Old 04-13-2009, 07:19 PM   #4
Rewards Points: 150
You got it, connect the neutral in the middle. Neutral and ground are bonded only at the box, you'll connect the ground at the same place or on the neutral bar. It ain't rocket science but make sure you get it right
johnnyboy is offline   Reply With Quote
Old 04-13-2009, 07:24 PM   #5
Rewards Points: 287
Thank so much. That is exactly as I did mine. I don't see the ground wire coming from the meter in your photo, though. Only the #4 copper from the ground rod? And yours looks much neater than mine.
Thanks again,
Russell
Old 04-13-2009, 07:45 PM   #6
UAW SKILLED TRADES
Stubbie's Avatar
Rewards Points: 2,652
The neutral lug kit is simply to allow you to feed a downstream sub-panel that requires a neutral in the feeder that is larger than what the neutral bars will accept. Or if the panel has feed thru lugs.
" One nice thing about the NEC articles ... you have lots of choices"
Stubbie
Old 04-13-2009, 07:55 PM   #7
UAW SKILLED TRADES
Stubbie's Avatar
The earth grounding depends on where the main disconnect is located. Is your panel main lug or main breaker? If it is main lug then where is your service disconnect? Out by the meter?
Stubbie
Old 04-13-2009, 08:02 PM   #8
Rewards Points: 287
I have a main breaker in the breaker box and out next to the meter. Is this okay?
Thanks,
Russell
Old 04-13-2009, 08:07 PM   #9
Rewards Points: 287
Also, there is a small clear mushroom shaped piece of plastic which came with the breaker box and I have no idea what it is for. Any ideas?
Thanks,
Russell
Old 04-13-2009, 09:08 PM   #10
UAW SKILLED TRADES
Stubbie's Avatar
It's ok but you really only needed a main lug panel. You should have 4 wires coming from the service disconnect out by the meter to the new load center...2 hots, the neutral and the ground. You should not have the main bonding jumper (green screw) installed thru the neutral bar of the new panel. Neutrals and grounds are kept unbonded. You only bond the neutral to the ground at the disconnect out at the meter. This is your service equipment not the the new panel. You only bond neutral to ground at the first means of disconnect. This is why you do not see the ground wire in the image posted. That is because the panel shown is the first means of disconnect (main breaker panel) and is fed by 3 wires from the meter. You have 4 wires because your service equipment is the disconnect at the meter not the new 150 amp panel.
Post a picture of the wiring of your panel so we can check things out.
You should also have earth grounding conductors going to possibly your metal water lines and a ground rod from the service disconnect.
Stubbie
Old 04-13-2009, 09:22 PM   #11
Rewards Points: 287
Thank You,
I'll post a photo tomorrow.
Russell
Old 04-13-2009, 10:50 PM   #12
Licensed electrician
Rewards Points: 1,738
It seems that the main breaker panels are cheaper than the lug only panels.
Old 04-14-2009, 08:12 AM   #13
Rewards Points: 2,350
Asking if you did it right after the fact is kind of a bass-acwards way of doing things. Let me explain how these threads usually end. OP posts question about something they've done. They aren't really wanting to hear that they may have done something wrong. They are really just looking for reassurance they did it right, and thus really won't hear it any other way. Someone tells them that something is wrong, and explains why. OP says "But it works??". Someone else explains why it may work but is still wrong. OP has already done the job and doesn't want to hear any of that, so disappears and is never heard from again, most likely leaving his hack job just the way he finished it ignoring the good advice he recieved.
Old 04-14-2009, 11:05 AM   #14
Rewards Points: 287
Not me. I have to have it right - even if it means doing it over. I am going to post some pictures. If the forum consensus is that I should do it over, then I will. It didn't take very long to do it the first time and if it's not right at least I will know what I've done wrong. I searched the net for quite awhile before I found this forum and I am thankful for the information contained herein and even more thankful that there are knowledgeable electricians out there willing to share their wisdom. If I had found the forum sooner, things would have gone smoother for me. I have read countless books on the subject of residential electrical practices and insist that all the work I do is up to NEC standards. But I haven't found any books which explain, in language that I can understand, how to install the breaker box. My next post will have the photo and I look forwrd to the forum critique.
Thanks,
Russell
Old 04-14-2009, 01:03 PM   #15
UAW SKILLED TRADES
Stubbie's Avatar
Thanks,
Russell
Well Russell you sound like someone worth helping IMO. While your getting the photo posted...ask us how if you have troubles...one of the first questions I have is what is the amp rating of the service main breaker out by the meter?
Stubbie
Garage Wiring issues jimmyfloyd Electrical 20 06-08-2009 02:57 PM
Next Question, Sub panel in detached garage... OmegaBunny Electrical 5 09-15-2008 11:37 PM
Sub panel sizing and distance question fburke Electrical 13 06-11-2008 06:33 PM
turn main panel into a sub panel? tikicarver Electrical 2 01-24-2008 07:37 AM
3 phase panel question curse21 Electrical 2 08-18-2004 10:17 PM