Split Receptacles - Reactive Loads - Electrical - DIY Chatroom Home Improvement Forum
Old 08-26-2012, 05:26 PM   #1
Split receptacles - reactive loads
A bit of a theory question.
From what I understand, split receptacles are allowed to share a neutral since the two hots come from opposite sides of the panel and are 180 deg out of phase. Therefore, for purely resistive loads, the current in the common neutral should never exceed the wire rating.
Question: What about reactive loads? If capacitive and inductive loads are present, it is theoretically possible that the current in the common neutral would exceed the rating of the wire.
How does the code deal with this?
zubor is offline   Reply With Quote
Old 08-26-2012, 05:33 PM   #2
E2 Electrician
stickboy1375's Avatar
Rewards Points: 2,970
if you were able to google that much, why not the rest?
Old 08-26-2012, 05:36 PM   #3
A "Handy Husband"
rjniles's Avatar
Rewards Points: 4,212
What type of these loads do you find in a DIY environment?
Coastal South Carolina
Old 08-26-2012, 06:09 PM   #4
Rewards Points: 826
It doesn't. The example you make is only theoretical. It is solved with simple trig functions. If the voltage on first phase is sin(x) and say you put a pure capacitive load on it the current will follow sin(x+pi/2), where the
+pi/2 is the current lead of a capacitor. On the other phase you put an inductive load on it the current will be sin(x-pi/2-pi), the -pi/2 is the lag of an inductor and -pi is the alternate phase (180 degrees out of phase).
We know sin(x+pi/2) = sin(x-3pi/2) therefore the magnitude of the current is exactly 2x the value of either branch.
Again the odds of a highly (i.e. near pure inductor) inductive load already are nil in a home, especially one at exactly the branch circuit current rating. Similarly highly capacitive and at the full branch circuit current is also low. The combined probability of these two loads then being on opposite phases of a single split duplex... come on, not going to happen.....
curiousB is offline   Reply With Quote
Split receptacles in kitchen sanec1 Electrical 30 05-13-2012 02:39 AM
installing 3 split receptacles Denisstjean Electrical 2 05-03-2012 09:10 AM
Wiring in New Addition? sandyman720 Electrical 6 11-27-2011 03:34 PM
Split receptacles, double pole breakers and multiple circuits in a junction box. morganhammer Electrical 6 04-05-2011 04:38 PM
1 switch split receptacles Price pfister Electrical 16 05-03-2007 09:01 PM