That motor will produce right around 4HP continuously. It is 240 volt only, it cannot be made to run on 120.
Since it was in service when it was removed, I strongly suspect it will run just fine as-is when connected to a 240 volt source.
Code-wise, 430.51 (short circuit and ground fault protection) plainly states that the rules in article 240 (overcurrent protection) do not apply. Table 430.52 lists the maximum breaker size as 250% of the current rating of the motor. When a motor is marked in amps but not HP, the nameplate amps is used. Otherwise, the tables in the back or article 430 are to be used.
Technically, the maximum rating of the breaker supplying this motor would be 40 amps.
If this were mine though, I would put the 50 amp plug on it and not give it another thought.
P.S. The minimum wire size for most motors (including this one) is 125% of the current as determined above. With motors, it's perfectly code compliant to have a small wire connected to a larger breaker. For example, a 1HP motor operated at 120 volts can be supplied by #14s (or larger), and they can be landed under a 40 amp breaker (or smaller).
Rob
P.S. The starting current (as listed on the nameplate) is 93 amps. This is about normal for a motor like this one. This is also why we're allowed to increase the breaker size for a motor. A small breaker might trip on starting. The overload protection of the motor also protects the wire to it.
All motors require a disconnecting means (with a few exceptions), a cord-and-plug meets this requirement.
micromind is offline   Reply With Quote
Old 01-08-2012, 06:43 PM   #17
Rob
I agree except I would at least #10 just because.
Hardway is offline   Reply With Quote
Old 01-08-2012, 08:12 PM   #18
Licensed Electrical Cont.
Speedy Petey's Avatar
Rewards Points: 1,956
Because....... you like to waste money?
Old 01-08-2012, 08:47 PM   #19
So if it cant be made to run on 120v = wont run at all, then it should be ready to go since I'm assuming it was in service when disconnected. I was confused with the L1 and L2 on the wire diagram on the nameplate vs. the wire configuration of the motor. There is an extra terminal in the motor towards the bottom that is not identified by the wire diagram. I may call Grainger tech. tomorrow to see what each terminal is designated for.
tsayyote is offline   Reply With Quote
Old 01-08-2012, 10:06 PM   #20
Idiot Emeritus
L1 and L2 are where the incoming power goes. It doesn't matter which wire goes where, as long as there's 240 volts across L1 and L2, it'll run.
Old 01-09-2012, 11:33 AM   #21
Well see so say you Speedy Pete. How about free? THHN 12ga to 6ga free, no cost. The motor won’t fail either.
Old 01-10-2012, 12:32 AM   #22
Alright, ao I've got everything working now. I stopped by the previous owner's shop and as predicted by a few of you, the plug was changed to a 125v plug to match his receptacle even though it was wired up for 240v. tsk tsk tsk! Got the compressor wired in without changing any wires in the motor and she fired right up.
Thanks for all of your support!!
The Following User Says Thank You to tsayyote For This Useful Post:
frenchelectrican (01-10-2012)
Old 01-10-2012, 12:36 AM   #23
" Euro " electrician
frenchelectrican's Avatar
Just make a habit when you get done with compressour open up the drain valve to get the water and other gunk out everyday if you run it alot otherwise end of the useage.
And with fixed ( stationary ) units I use a rubber mat below the mounting feet the reason why I do that due cut the noise down a little and also give the tank some wiggy room to expand and contract a little.
Enjoy your compressour.
Merci,
Marc