SPA Wiring - Electrical - DIY Chatroom Home Improvement Forum
Old 10-22-2008, 07:59 AM   #1
SPA Wiring
I recently replaced my disconnect box on the outside of my house for my spa. After doing that, when flipping the breaker on it immediatly trips. If I remove the white nuetral wire from the spa box, i can turn the tub on and it works. Is this supposed to be that way, or am I doing something wrong?
Thanks,
Brent
bburtrum is offline   Reply With Quote
Old 10-22-2008, 08:11 AM   #2
Electrical Contractor
jbfan's Avatar
Rewards Points: 478
You have the ground and neutral tied together at the spa box. Is your spa a 240v or is it 120/240?
Remove all the wires and take a picture where the wires are connected to the spa.
jbfan is online now   Reply With Quote
Old 10-22-2008, 08:22 AM   #3
It is a 240v system. Where should the white wire go at the SPA box?
Old 10-22-2008, 08:25 AM   #4
jbfan's Avatar
Rewards Points: 478
If it is 240v then you do not need the white wire, howecer the ground wire needs to ne insulated. Did you strip the outer jacket of a peice of romex?
Old 10-22-2008, 08:43 AM   #5
By ground wire do you mean the bare copper wire? If so, that is all one bundle, there was the white, the red, the black, and a bare copper all bundeled together.
If you do not use the white wire does that prevent the GFCI from doing its job?
Old 10-22-2008, 08:48 AM   #6
This is kind of out of code, but he could move the insulated white to the ground bar and mark it green if it's 240V. It does look like stripped NM wire though. Pretty sure it's not THWN. What happened to the bare ground at the spa? If you look at the label under the wires, it has the Ground and two hots marked.
To do this correctly, the whole thing needs to be redone.
jerryh3 is offline   Reply With Quote
Old 10-22-2008, 08:58 AM   #7
I am much more converened with Safety than I am with code. It sounds to me like I could leave the white connected to the ground at the spa box, then move the other end of it from the neutral bar in the disconnect box to the grounding bar in the disconnect box.
The bare copper wire goes to a grounding bar on the outside of the SPA box, it is outside of the pictures view.
Also, can someone give me a link to the type of electrical cable I should be using for this?
Old 10-22-2008, 09:38 AM   #8
Rewards Points: 160
At the spa box, put the white on one of the unused terminals, one of the two on the right. Connect the ground from the disconnect to the green ground terminal in the spa box. You say you have the ground outside the box, but I see a ground terminal inside on the far left. This is where it goes. The terminal outside the box is most likely for a bonding grid.
If your spa is located on the ground, on pavers or on concrete, it must have a bonding grid installed.
The disconnect must be in view from inside the spa and be readily accessible.
Old 10-23-2008, 06:56 AM   #9
Just wanted to let everyone know that I moved the white wire coming from the SPA out of the GFCI breaker and into the grounding bar on the left side of the SPA box in the picture shown. Now everything works great and the GFCI breaker works correctly.
Disclaimer: This is not up to code, but is safe.
Old 10-23-2008, 07:11 AM   #10
This is NOT safe. Why do they have code? To keep people SAFE. People like you shouldn't be doing ANY electrical work!
rgsgww is offline   Reply With Quote
Old 10-23-2008, 07:14 AM   #11
You actually use conduit with thwn wires.
Old 10-23-2008, 07:42 AM   #12
lol, what makes it not safe?
I'll also have to disagree with you, most electrical work a educated homeowner can perform. I agree, there are some things that require a licensed electrician, but simple wiring does not.
Old 10-23-2008, 07:48 AM   #13
I'll also have to disagree with you, most electrical work a trained monkey can perform. I agree, there are some things that require a licensed electrician, but simple wiring does not.
If it's so simple, why couldn't you figure out that simple problem? The terminals were clearly marked and you still had it wired wrong.
Old 10-23-2008, 07:53 AM   #14
Again, i think i did figure out my problem before coming here, I asked on here for suggestions of what I could do.
Also, don't tell anyone, but my disconnect box is within 5 feet of the tub, it is 4 feet away! According to code, 5 feet is safe, and 4 feet is not. (in Michigan)
Old 10-23-2008, 07:58 AM   #15
Yes. That really sounds like you had the problem figured out. Good luck in the hot tub.
Wiring diagram for three-way switches with pilot light SaxTeacher Electrical 34 09-15-2013 07:53 AM
Wiring Sequence on Adding a New Outlet kennykenny Electrical 9 06-09-2008 02:06 PM
Replacing wiring in middle of run, ungrounded lighting circuit alexz Electrical 3 07-05-2007 08:53 PM
Knob & Tube wiring - How concerned should we be? hotdiggitydog Electrical 6 04-11-2006 07:52 PM
Garage - Protecting wiring installation eastment Electrical 4 11-26-2005 11:52 AM