Old 04-24-2007, 04:25 PM   #1
Spa Hook Up Questions
Hi Board, (Location - California)
We are anticipating the delivery of our Hot Spring
Envoy SPA and planning the electrical work.
The owners manual states that the waterproof conduit
connects to the IQ 2020 control panel using a 3/4"
liquid tight flex conduit fittings. The cable run
(through water tight plastic conduit) between the GFCI
30/20A breaker box and the IQ 2020 requires four #10
AWG wires and two #12 AWG cables, the local code
states that the conduit cannot be filled by more than
40%.
So my questions are:
1) Would these 6 wires occupy < 40% of a 3/4" conduit?
(I was planning to use 1" conduit but am concerned
that I will have a problem connecting it to the SPA)
2) What size conduit have other Hot Spring owners
used?
3) Is there some kind of waterproof reducer I can use
to get down to the 3/4" size that the control box
calls for or will a 1" conduit also fit the IQ 2020
controller?
4) We plan to use THHN cable in the watertight
conduit, I read that multi strand is best for this
application because its compressible when you tighten
down the screws, is this good information?
5) We plan to use 6/3 Romax cable for the run from the
main breaker box to the GFCI 30/20A breaker box, does
anyone know what gauge the solid earth wire is on this
type of cable? (the Hot Spring spec calls for #10
AWG).
Many thanks in advance...appreciate any reply :-)
aguamarina4u is offline   Reply With Quote
Old 04-24-2007, 07:50 PM   #2
zel
Send a message via AIM to zel
I'm sorry I dont have the answer you need, but if you cant find it here, try on www.spaforums.com I found alot of spa info there when I needed it. Good Luck.
zel is offline   Reply With Quote
Old 04-24-2007, 07:55 PM   #3
Electrician
1. I am thinking THHN is the same as T90, i could be wrong and if i so i
am sorry. For T90 you can fit 10 #10 in a 3/4 so your 4 10 and 2
12 will be fine. Remember you will also need to run a ground in that
plastic pipe as well.
3. Should not be a problem, but you would never do this because you
still will only be able to use the calculation for 3/4 due to that
reducing washer.
Thats a start can't answer #5 for you because I have no clue.
Darren
darren is offline   Reply With Quote
Old 04-24-2007, 08:19 PM   #4
Licensed Electrical Cont.
Speedy Petey's Avatar
Here is a copy of my reply to you in another forum:
Considering you legally fit 10 - #10THHN conductors in 3/4" Liquidtite, your seven is fine.
The rest of your plan seems fine as well.
6/3NM has a #10 ground.
Remember, you can ONLY use the NM cable for the inside wiring portion of this circuit.
Old 04-25-2007, 12:15 PM   #5
Thanks, I appreciate the input!
Old 04-25-2007, 12:36 PM   #6
I thought you could only put three current-carrying conductors into any one conduit. Did I misunderstand that part?
NateHanson is offline   Reply With Quote
Old 04-25-2007, 12:46 PM   #7
YES. Very much so.
Old 04-25-2007, 12:52 PM   #8
Well, wouldn't be the first time. :o
Old 04-25-2007, 05:34 PM   #9
Electrician
Hey Nate
When you have more then 3 wires in a pipe you have to derate them, for they carry less current. This is where you may be getting confused. If you have a 6 inch pipe you are able to put up to 200 #12, I still want to see someone do this.
Darren.
Old 04-25-2007, 06:33 PM   #10
Yes, that's it darren. I looked up where I read it and it was the ampacity table.
Still wrong, but at least I didn't totally imagine it.