Spa disconnect / GFI confusion among other things
Hello,
I can't seem to get a consistent answer to this question just surfing web.
DO I or DO I NOT need a manual disconnect / cutoff no closer than 5 feet and within line of sight ?
Everything seems to conflict.
I will have a dedicated sub panel somewhere close to spa with a GFI 60 amp breaker.
Some places say that IS the disconnect.
Some places say I need the disconnect AND the GFI breaker. So confusing.
I think NEC says disconnect doesn't apply to single family dwellings.
Please help.
Also, a couple easy questions.
1) Does sub panel have to be mounted a certain height or distance from ground / roof ?
2) Spa requires 6 AWG which is what I was planning to use. What size ground should I use ? 6 AWG or maybe #8 or #10 ?
3) Code says I cannot have an outlet within 10 feet of spa. Can I just replace cover with a plate / blank or do I have to physically unhook power supply ?
4) I will be installing an outlet in my BBQ island. I plan to use UF for the 15 feet it needs to go underground. I was told I can continue to use the UF
inside the island as long as I stapled it to the structure and didn't just leave it laying on ground.
Is that correct ?
5) Does outside outlet need to be a GFI outlet or will a standard out be ok ?
6) I was planning to use a 12/2 regarding the island. 12/2 and a 20 amp breaker ok ?
Thank you very much in advance.
Much appreciated.
Maxian is offline   Reply With Quote
Old 11-09-2012, 06:23 AM   #2
Electrical Contractor
kbsparky's Avatar
Hello,
You do need a disconnecting means.
Please help.
You are confusing a disconnect with an emergency stop switch (Panic button). You do not need the panic stop button at a single dwelling. You still need a disconnecting means. The GFI breaker can serve as the required disconnect if located within sight as mentioned earlier.
I prefer to mount it a couple feet off the ground, to prevent water splashing in during heavy rains.
If specified by the manufacturer, then follow their instructions. If not specified, then a #10 ground is all that is required.
Blank off any non-conforming outlets. Just wire-nut the conductors to maintain continuity of the circuit.
Is that correct ?
Correct.
GFI protection is required. Whether this is done by a GFI breaker, or the actual receptacle is up to you.
Sounds like a plan.
Much appreciated.
-KB
The Following User Says Thank You to kbsparky For This Useful Post:
Maxian (11-09-2012)
Old 11-09-2012, 08:09 AM   #3
Licensed Electrician
k_buz's Avatar
Rewards Points: 2,006
This is not true according to the NEC. The code states you cannot have any receptacle within 6' of the spa/hot tub and you MUST have a GFI protected recept outside of 6' and within 10' of the inside wall of the tub.
Old 11-09-2012, 08:40 AM   #4
Thank you for your time
Old 11-09-2012, 02:13 PM   #5
Rewards Points: 324
see 680.43(A) min is 5 feet and not exceeding 10 feet from inside wall of spa.
oleguy74 is offline   Reply With Quote
Is voltage rating of 4-pole disconnect switch per pole? CDragon Electrical 5 11-07-2012 03:31 PM
Question: Backfeeding Gen thru Pull-Out Disconnect and GFCI (with interlock kit) diyfram Electrical 7 11-02-2012 11:59 AM
small solar disconnect switches rescrewableE Electrical 1 01-02-2010 08:55 PM
Main disconnect neutral wiring Daniel Holzman Electrical 5 10-04-2009 02:36 PM
Wiring AC unit through 20A Disconnect whirly Electrical 5 04-26-2009 10:40 PM