-   -   Solve this one (http://www.diychatroom.com/f18/solve-one-168797/)
jlmran 01-10-2013 08:41 PM
Solve this one
3-way switch
Switch in position 1:
Black traveler terminal = 62v
Red traveler terminal = 120v
White common terminal = 120v
Switch in position 2:
Black = 0v
Red = 120v
White = 0v
All values referenced against the bonding conductor. Haven't opened up the other 3-way switch or the lights. Lights and switches appear to be functioning normally.
Where does the 62v come from?
jlmran 01-10-2013 08:55 PM
Deleted
Missouri Bound 01-10-2013 09:09 PM
Other than your voltages....what's the issue with the switches?:whistling2:
jlmran 01-10-2013 09:14 PM
Unbonded while having metal covers. I learned of the voltages while verifying presence/absence of voltage. Unbonded status is now resolved. Why are you whistling?
AllanJ 01-10-2013 09:32 PM
Red traveler is energized by the other switch.
Position 1 -- This switch connects white common to energized red. Your meter is sensitive enough to pick up phantom voltage induced in isolated black from red juxtaposed in same cable, voltage relative to bonding conductor.
Position 2 -- The switch connects white common to unenergized black traveler. Any phantom voltage is dissipated to neutral through load (light) at far end of white wire.
Wire color usage is incorrect. The white wire should not be used to go from the switch to the load. In this case you would need to use the white wire as a traveler.
dmxtothemax 01-10-2013 10:46 PM
Originally Posted by jlmran (Post 1090685)
3-way switch
Black = 0v
Red = 120v
White = 0v
Phantom voltage caused by close proximity to energised conductors !
Put a test lamp on it and I bet it goes away !
joed 01-10-2013 11:06 PM
Agree with the above. No problem with the voltages. The switch is working properly. The 62 volts is phantom and not important.