#1 |
Sizing wire for sub-panel.
I am running to a subpanel in a workshop 30 ft from my house. My house service is 200 amp. I plan to run a total of 135 ft to the workshop from a 60 amp breaker in my main panel with either 6-3 copper, or 2-3 aluminum to a sub-panel. 30 ft of the run will be underground, which I can put in conduit. If I can get the aluminum for less than the copper, should I go with that?
#2 |
I'm not an AL fan, especially underground.
And, will #2 fit in the 60A breaker lugs? And, you won't be using 6/3 in the conduit (unless it's underground rated wire), you will be using three #6's and a #10 ground (THWN). |
#3 |
Why could I not use interior 6-3 with ground if I put it in conduit?
#4 |
Xtreme DIY'r
It must be rated for wet conditions- buried
THWN is rated for wet use - NMB is not |
#5 |
Sizing wire for sub-panel. |
#6 |
The wire I am looking at on Craigslist is described as " #2 ALUMINUM TRIPLEX OVERHEAD OUTSIDE WIRE ". Does this sound like wet rated wire? Could I put this in conduit?
#7 |
electrical contractor
It is probably wet rated, most tri-plex is, but you will have to add the ground conductor, and runn it in conduit if it is not rated for direct burial.
Jimmy Life is tough, Life is tougher when you are stupid. |
#8 |
Do you mean that I would either have to use underground rated 6-3 wire or use separate threaded #6 wires plus gnd (#10?)in conduit? Once inside the house and workshop, I would still have to use conduit to protect the conductors, right?
#9 |
Xtreme DIY'r
Option 1 - direct burial wire with 4 wires
Option 2 - individual wires in conduit, entire run Option 3 - cable with required wires in conduit, conduit sized for cable In all options the wire must be wet rated |
#10 |
My License Ain't 4 Sale..
"Overhead" triplex likely has a bare neutral, so running it through conduit underground is out of the question.
| Display Modes | |
| Heat Shrink on Bare Ground wire in Panel | jamiedolan | Electrical | 5 | 01-17-2009 04:40 PM |
| Wire size for Sub panel | DaleB | Electrical | 13 | 09-18-2008 01:28 AM |
| Melted Service Entrance Wire in Panel | theatretch85 | Electrical | 13 | 08-22-2008 11:37 AM |
| Sub Panel and Wire Guage | budhead | Electrical | 14 | 08-19-2008 05:18 PM |
| Pool Sub Panel wire / conduit questions | Al the Diy guy | Electrical | 23 | 02-03-2008 03:32 PM |