Old 12-23-2011, 08:51 AM   #1
vmw
sizing electrical wire for amps
need to run electric to machine . 240 volts 3 phase 100 amps max load. need to know size of wire and size of conduit to use . our power comes from a busduct
vmw is offline   Reply With Quote
Old 12-23-2011, 09:21 AM   #2
Average Joe/ex-Navy IC3
gregzoll's Avatar
Here is a good motor calculator http://www.jandlelectric.net/motorcalc.html You did not state horsepower, and using this one http://www.engineeringtoolbox.com/el...tor-d_832.html I am coming up with 43hp. Here is a whole list of different calculators http://www.electrician2.com/calculators/elcal.html which are all really good.
: Now listen, Cadet. I've got a job for you. See this button?
: Don't touch it! It's the History Eraser button, you fool!
: So what'll happen?
: That's just it. We don't know. Maybe something bad, maybe something good. I guess we'll never know, 'cause you're going to guard it. You won't touch it, will you?
The Following User Says Thank You to gregzoll For This Useful Post:
CaptainD51 (12-23-2011)
Old 12-23-2011, 09:45 AM   #3
100 amp wire ampacity NEC 2011 310.15 (b)(16) CU 90 degree 3 AWG, AL 90 degree shows 2 AWG, 8 AWG CU for equipment ground, 6 AWG AL 2011 NEC 250.122
This is calculated on THWN / THHN
CaptainD51 is offline   Reply With Quote
Old 12-23-2011, 09:53 AM   #4
Fill capacity for EMT conduit, 3 AWG needs 1 1/4" (6 Max conductors, 3 for 1" so not be enough room), 2 AWG in 1 1/4" EMT show 5 max conductors
2011 NEC Chapter 9 tables 1, 4 and 5
Old 12-23-2011, 10:39 AM   #5
Licensed Electrical Cont.
Speedy Petey's Avatar
Hire an electrician!!
This is NOT DIY work and you should NOT be messing with it if you are not a qualified electrician.
The Following 3 Users Say Thank You to Speedy Petey For This Useful Post:
DexterII (12-23-2011), Jim Port (12-23-2011), plummen (12-23-2011)
Old 12-23-2011, 11:24 AM   #6
Licensed electrician
Unless the terminals are 90 degree rated you would need to use the lesser ampacities of the 60 or 75 degree columns.
Old 12-23-2011, 12:45 PM   #7
wareagle's Avatar
Thumbs down
CaptainD, you can not use the 90C rating when sizing conductors. You must use the 75C rating and sometimes the 60C rating of conductors.
wareagle is offline   Reply With Quote
Old 12-23-2011, 02:07 PM   #8
Ummmmm.....
Old 12-23-2011, 03:27 PM   #9
I Think I hear an echo.
gregzoll (12-23-2011)
Old 12-23-2011, 03:46 PM   #10
wareagle's Avatar
They do sound similar. Maybe the captain needed a double wham-O.
Old 12-23-2011, 05:20 PM   #11
Not to argue, I’m learning myself, why is that?
Most THHN/THWN that I’ve seen has 90 degree markings on it. Are terminals not rated to that temp or is there a standard I have not read that indicates 75 degrees?
Note: At 75 degree for 100 amp, CU still shows 3 AWG but it is right at 100 amp, AL drops to 1 AWG
Would that be correct or am I missing something ?
Old 12-23-2011, 05:24 PM   #12
Electrical Contractor
kbsparky's Avatar
Special rules apply to motor circuits' conductors sizing and overcurrent protection.
We need to know the hp and voltage ratings of the motor(s) in order to make a proper calculation.
It's possible that a motor could be supplied with a conductor capable of handling 50 Amps, but can be fused (or circuit breaker) protected at 100 Amps or more. 240.4(D) does not apply when dealing with motors, etc. You have to begin at 240.4(G) ....
More info is needed here ... (and you're right, this is NOT a DIY project!)
-KB
The Following User Says Thank You to kbsparky For This Useful Post:
Old 12-23-2011, 05:27 PM   #13
kbsparky's Avatar
... am I missing something ?
Yup. Unless marked with a temp rating, all equipment is assumed to be rated for 60C terminations. Most circuit breakers, controllers, etc are marked at 75 C
There is not much out there listed for 90 C terminations (which is pretty hot, and would burn you if you touched it).
-KB
re-use electrical wire? cbzdel Electrical 9 06-01-2010 08:44 PM
Low voltage wire & electrical wire (NM) dyang Electrical 3 05-04-2010 11:02 PM
Running electrical wire into 98 Buick Lasabre Red Squirrel Automotive Repairs 5 04-22-2010 10:08 AM
Cap electrical wire? oscarMadison Electrical 5 03-01-2009 10:26 PM
wire sizing for wall heater? gerhops Electrical 22 09-21-2008 10:59 PM