Size Of Wire For A Dryer - Electrical - DIY Chatroom Home Improvement Forum
Old 11-17-2009, 08:09 PM   #1
size of wire for a dryer
Should wire be 10 guage , fused at 30 amps, or should it be 8 guage wire.
den6200 is offline   Reply With Quote
Old 11-17-2009, 08:14 PM   #2
Should dryer wire be 8 or 10,guage wire ?
Old 11-17-2009, 08:18 PM   #3
How far is the wire run ?
Usually 10-3 is all you need w/30a breaker
Old 11-17-2009, 08:24 PM   #4
300zx's Avatar
Post
As everybody has said 10-3 on 30 amp breaker
300zx is offline   Reply With Quote
Old 11-17-2009, 08:31 PM   #5
10 ga. copper,
less than 5% voltage drop at 25A,
you could put the dryer up to 120' from the panel.
Old 11-17-2009, 09:00 PM   #6
Idiot Emeritus
Rewards Points: 1,492
10/3 with ground. 4 wires total. Black, red, white, and a bare ground. 30 amp two pole breaker.
4 wire receptacle. NEMA # 14-30. The white goes on the L shaped terminal, ground goes on the round terminal, black and red go on the straight terminals. It doesn't matter which one is black and which is red.
If the dryer has a 3 wire cord, remove it and get a 4 wire one. It'll have the L shaped prong that matches the receptacle.
On the terminal board in the back of the dryer, black goes on the left, white goes on the center, red on the right, and green goes under a screw on the frame. If there's a jumper from the frame to the center terminal, remove it.
This is the safest possible way to hook up dryer.
Rob
micromind is offline   Reply With Quote
Old 11-17-2009, 09:10 PM   #7
Also it is a good idea to look at the installation manual for appliances. In some cases appliances can be different amperages and call for different amperage breakers depending on the model. I don't think this is the case with dryers, but good to double check anyway.
Billy_Bob is offline   Reply With Quote
Old 11-17-2009, 09:51 PM   #8
General Contractor
Another vote for 30A 10 gauge, that's all I've ever seen for a dryer.
KennMacMoragh is offline   Reply With Quote
Proper awg wire size to use? Suzuki91vx800 Electrical 36 06-23-2009 04:18 PM
wire size for ac/heating forced air unit macfluke Electrical 2 03-04-2009 12:29 AM
wire size for solar generator? krisman Electrical 12 01-28-2009 10:34 PM
wire size suggestions dkennedy Electrical 17 10-19-2008 04:09 PM
Dryer Grounding??? Traci_howdyadothat Electrical 7 05-27-2008 01:14 PM