Old 07-11-2012, 04:45 PM   #1
Size of wire and breaker
I am installing a couple of 60watt lights and a sprinkler control box and a small water feature pump. i will have a run of about 325 feet. what size of wire and what size of breaker for the main run to a small sub panel with 3 breakers of 15 amps for the lights, sprinkler and fountain pump?
dwagg is offline   Reply With Quote
Old 07-11-2012, 04:52 PM   #2
Doesn't seem like this would draw much so three 15A circuits sounds like overkill. Do you know power draw of fountain pump? Sprinkler controller is probably less than 25W.
I think a single 14-2 UF cable fed by a single 15A breaker with a GFCI receptacle instead of a breaker panel at the remote point then slave the lights, pump, and sprinklers off of the load side of the GFCI. You get a 120VAC outlet as an extra bonus.
curiousB is offline   Reply With Quote
Old 07-11-2012, 05:21 PM   #3
E2 Electrician
stickboy1375's Avatar
If I'm digging 325', I'm installing conduit, and leaving provisions for the future, without seeing what you are actually doing, I might pull #6AWG, to a remote panel...
Old 07-11-2012, 05:27 PM   #4
Master Electrician
Go big or go home lol. Probably need a number 6 anyways at that distance. Taking a random number of 8a you would need a number 8 wire to get it out there.
Sarcasm is my friend
I'm here to learn too, i do mostly commercial/industrial/new construction and this place is a great way to pick up tips on residential from some good electrical minds. Excuse the spelling, my phone has a mind of it's own.
andrew79 is offline   Reply With Quote
The Following User Says Thank You to andrew79 For This Useful Post:
stickboy1375 (07-11-2012)
Old 07-12-2012, 10:55 PM   #5
Julius793's Avatar
Make sure you install pull Boxes if there are to
many 90s
Electricity will kill you if you give it a chance
Julius793 is offline   Reply With Quote
What size wire and breaker needed? stlouistruckn1 HVAC 4 02-06-2012 10:35 PM
wire size vs breaker size Jimster 481 Electrical 3 08-20-2011 10:41 AM
Wiring Size Calculations for New Service CorinthWest Electrical 7 12-07-2010 12:36 PM
hooking up dryer....bronx ny code SURFBUG Appliances 6 10-14-2008 10:41 PM
Wire size and Breaker size for remodel ?? Skydmark1 Electrical 12 12-15-2007 06:00 PM