single-pole switch trips breaker
I am replacing a single pole switch that controls an outlet on the same the wall. After replacing it, every time I flip the switch the breaker trips. There are 2 wires (one black and one white) and a ground wire. From testing, I can tell the white wire also carries a current. Any ideas of what could be causing the breaker to trip?
Annapolis, MD is offline   Reply With Quote
Old 02-17-2010, 04:45 PM   #2
Electrical Contractor
jbfan's Avatar
Rewards Points: 482
How did you hook the switch up?
jbfan is online now   Reply With Quote
Old 02-17-2010, 05:16 PM   #3
joed's Avatar
Rewards Points: 12,892
How did you connect the switch? Did you make any changes at the receptacle?
Old 02-17-2010, 05:39 PM   #4
I connected the switch with the black wire to one brass screw, the white wire to the other brass screw, connected the ground to the ground screw. I did make a change at the receptacle. When I replaced the receptacle, I noticed that one set of wires (one black, one white) were capped off and not connected to the receptacle. The wires looked ok and carried a current, so I connected them to the receptacle. The receptacle works when I plug something into it, I just can't control what I plug in with the switch because of the breaker tripping.
Old 02-17-2010, 07:24 PM   #5
wirenut1110's Avatar
Rewards Points: 510
Send a message via AIM to wirenut1110
Disconnect the black wire that was on the receptacle and wire nut it to the white wire that was capped off.
The black wire that was capped off should be on the brass screw and the original white wire that was on the receptacle should be on the silver screw.
The white wire that was capped off is not a neutral and when you turn on the switch you are creating a dead short.
The way I described is if you want to switch the whole receptacle. If you want to switch half of the receptacle, post back.
wirenut1110 is offline   Reply With Quote
Old 02-17-2010, 08:28 PM   #6
joed's Avatar
This is where you went wrong. It is a common mistake. People see the mismatched colours and think OH I better fix that. That black wire and white was the power connection to the switch. The other black wire brings switched power back from the switch.
What you did was connect the switch directly across the hot and neutral when you made the change.
Old 02-17-2010, 10:39 PM   #7
Rewards Points: 1,514
In the receptacle box ...
The black wire coming back from the switch should be connected to a gold screw of the receptacle (on the side with the narrower prong holes). The white wire comingfrom the panel (from the other cable) should be connected to a silver screw of the receptacle. Wire nut the other two wires (black from the panel, white from the switch) together.
The white to the switch should have a band of black or red tape or stain visible at both ends.
This is the way it should have been before you started.
AllanJ is online now   Reply With Quote
Old 02-23-2010, 09:11 AM   #8
Thank you
Thanks so much for the feedback. I'm going to attempt to correct my mistake today!
Old 02-26-2010, 11:32 AM   #9
It worked!
Thanks, especially AllanJ, for the explanation. I made the change and the receptacle and switch are working perfectly.
Single Pole vs. Double Pole Thermostat dforeid Electrical 14 08-26-2012 08:12 AM
New Fluorescent Ballast trips GFCI Breaker?? marc515 Electrical 7 02-18-2010 04:42 PM
900W and up trips breaker, Circuit draws power even with everything off... jasonblu Electrical 40 12-09-2009 02:29 PM
Adding a single pole switch to 3 way switch. adrien2 Electrical 6 05-28-2009 02:44 PM
when would a single pole switch... fabian Electrical 12 01-07-2009 08:19 PM