Siemens Sub Panel Wiring - Electrical - DIY Chatroom Home Improvement Forum
Old 04-04-2012, 12:00 AM   #1
I was doing research online and figured a post here would be helpful.
We need to wire in a sub panel for a basement project. The new expansion will support 4 new circuits and an oven.
The main panel is a Siemens with a 200A main. I stopped by Lowe's this evening and picked up a 125A 16 Place Siemens Sub Panel in the hopes of saving a few breakers that will be displaced by the feeder.
While I was there I also picked up up some knockout restraints, a 100A breaker, 10" of 3 conductor AL2/AL4 wire.
For a sanity check, I am planning on connecting the two 2 Ga. AL wires from the new 100A breaker in the main box to the lugs on the new sub panel. I will also use a 4 Ga. AL wire from the Neutral bar on the right side of the main panel (near where the solid copper ground is connected) to the Neutral Bar (green post) on the right side of the sub panel. Does the ground need to be extended as well? How should that be completed? Also, there is no good connector for the neutral wire on the sub panel, do I need an accessory like the ECLK2?
Also, is a conduit required between the boxes?
Please take a look at the pictures, let me know what I'm missing and thanks in advance.
Thanks,
Ryan
Siemens Sub Panel Wiring-img_0830.jpg   Siemens Sub Panel Wiring-img_0831.jpg   Siemens Sub Panel Wiring-img_0832.jpg   Siemens Sub Panel Wiring-img_0835.jpg
drunkboating is offline   Reply With Quote
Old 04-04-2012, 12:32 AM   #2
Electrical Contractor
rrolleston's Avatar
Rewards Points: 1,012
Send a message via AIM to rrolleston Send a message via Yahoo to rrolleston
Easiest way would be with 1/0 SER 4 wire cable because you are required to run 4 wires and also you will have to put that 100 amp breaker in a spot that has a smaller breaker a across from it because those panels are limited to 100 amps per stab on the bus.
You can't run separate wires without conduit and there has to be four conductors.
With Electricity there is the right way to do it and the dead way. Just because it works does not make it safe.
rrolleston is offline   Reply With Quote
Old 04-04-2012, 12:33 AM   #3
Licensed Electrician
k_buz's Avatar
Rewards Points: 2,006
Thanks,
Ryan
You cannot use the 3 conductor SE cable to feed the new subpanel. It must be 4 wire (2 hots, neutral, and ground), pipe between the panels in metal conduit and run 3 individual conductors, or pipe PVC between panels and run 4 individual conductors (2 hots, neutral, and ground).
In all of these cases the neutral must be insulated and sized the same as the hot conductors. The only conductor you can downsize is the ground.
Old 04-04-2012, 12:41 AM   #4
k_buz's Avatar
1/0 is overkill the max you would need is #1, maybe #2 depending on the type of wire contained in the cable.
You are not required to run 4 wires by the NEC. I've seen this stated numerous times here and its simply not true. You are required to have a ground present, but you do not need to pull a ground if the panels are connected by EMT or RMC.
If there is a 100A breaker installed, you cannot have any breakers on the same stab.
Old 04-04-2012, 12:51 AM   #5
rrolleston's Avatar
1/0 SER is what I would use if the person don't want to pay for conduit to be fitted between the two panels. It's only about $1.75 a foot
I doubt he is going to be cutting or bending EMT or RMC.
You can have another breaker on the same stab as the 100 amp breaker as long as the calculated load is under 110 amps. 15 amp breakers across from it should be fine.
Old 04-04-2012, 01:07 AM   #6
k_buz's Avatar
It may be what you would install, but its not required. Why tell someone to get something 2 sizes larger than what is required?
But you don't know that. The panels could be right next to each other and a EMT nipple might be even easier than SER. I don't see how it is a good idea to tell someone something is required when it isn't.
I disagree. While there might not be 100A on the stab when he first installs the breaker, what's to say its not going to be loaded to 100A in the future? I think you have to look at it as the total possible loads on that stab. I believe this is manufacturer specifications so I don't think we will find anything in the NEC on this subject. We could just agree to disagree on this one.
Old 04-04-2012, 01:45 AM   #7
The panels will be installed right next to each other. If a section of EMT will be conducive enough to keep from having to wire in yet another connection I'm all for it. Ultimately I'm not trying to over engineer it, just keep my kids safe.
Old 04-04-2012, 01:50 AM   #8
k_buz's Avatar
I would get a short 1 1/2" or 2" EMT nipple, 2 EMT connectors, 2 plastic bushings, and run 3 conductors...2 hots and 1 insulated neutral (tape the neutral with white electrical tape). The ground would be carried by the nipple. Then you don't have to get an additional lug to fit the ground to the ground bar.
Be sure to remove the boding jumper going from the neutral bar to the back of the sub panel.
The Following User Says Thank You to k_buz For This Useful Post:
Ravenworks (04-04-2012)
Old 04-04-2012, 09:00 AM   #9
Rewards Points: 324
just run a #8 green for ground.all you need and it will fit the buss.
oleguy74 is offline   Reply With Quote
The Following User Says Thank You to oleguy74 For This Useful Post:
Speedy Petey (04-04-2012)
Old 04-04-2012, 10:19 AM   #10
Licensed Pro
The #2Al is too small for the 100A breaker. Either use a 90A breaker or upsize the wire to #1Al or #3Cu. For that short a distance, I'd use Cu.
Tags
eclk2 , feeder , siemens , subpanel
Sub Panel GND and mixed 240/120 VAC branch curiousB Electrical 12 01-17-2012 11:49 AM
Wiring a sub panel ZBat910 Electrical 6 01-08-2012 03:00 PM
sub panel wiring grapeman Electrical 25 09-10-2011 09:48 PM
Structured Wiring Panel Location...Fire Rated Wall??? RICKM15752 Electrical 0 04-20-2011 12:30 PM
Getting a new 200A breaker panel Any brand better than other? GE? Siemens? twilightcall Electrical 4 01-22-2008 08:57 PM