Shock Problems, From Subpanel - Electrical - DIY Chatroom Home Improvement Forum
Old 06-14-2009, 11:44 AM   #1
Shock problems, from subpanel
SO I changed my homes service from an old 60amp to a new 200 amp service, from this panel, a 2 wire service goes to an old barn. One hot, One Neutral. goes from breaker and neutral in house panel up side of house and hooks on the 2 outside wires that run overhead to the barn.
Not knowing which one was which outside when I hooked them up. I took a chance and everything is fine.
I thought if I put the hot on the wire going to the barns ground, the breaker should trip. Right?
From the barns panel, everthing is fine. I think.
I have a circuit that goes to a switch and a gfi outlet. The other day I was running a submersible pump, got shocked when I touched the metal on the pump, thought it was the pump.
Then yesterday I got a tingle when I touched the metal box that the pump was plugged into. Checked it today, couldn't reproduce the tingle.
Later today, I plug a different pump in, and got a shock when I touched any metal part on the pump.
The GFI never tripped. I thought may be a bad ground in the metal box, or could I have crossed wires up when I ran the new wire to the barn feed? Thanks
WesternNY is offline   Reply With Quote
Old 06-14-2009, 12:15 PM   #2
DIY'r
ScottR's Avatar
Sounds like that's what happened -- hot and neutral are reversed. Maybe your neutral is bonded to the ground at your sub panel, but you have no fault path back to earth or the main panel.
You can get a receptacle tester @ most home centers/hardware stores for about $5 that would tell you for certain. It's a good tool to have around anyway.
ScottR is offline   Reply With Quote
Old 06-14-2009, 12:31 PM   #3
Rewards Points: 160
You have no ground and this quite dangerous.
No its not. All your receptacles are not correctly polarized. Lamp socket shell are now hot , possibly.
What ground? Two wires indicates you have no ground. If you have a ground rod out there it must be connected to the main service bonding grid (rod and water line) at the main panel and outside service. The ground (EGC) is what carries the fault current and trips the breaker.
The panel is non-compliant if it does not have a 3 or 4 wire feeder. If you are on the 2005 or earlier code cycle 3 wires are sufficient. But I would never pull a 3 wire feeder period.
You have no "Low Impedance" path for ground faults to go to. You are taking unnecessary and potential lethal dose of electricity if you do not correct this setup, bungled job.
Do not try to reproduce the tingle. It may be your last.
No, grounding system. Thats your problem.
GFCI's work without a ground present. Thats why you see no issues with your GFCI receptacle.
For the time being feed the GFCI first. This will protect you until you can get this corrected.
Old 06-14-2009, 12:39 PM   #4
I thought I would be a retired rock star at age 30.
We were both wrong.
Your polarity is reversed but simply swithing it won't fix all your problems, it will just make the symptoms go away. You also probably have a bootlegged ground somewhere.
You need to get a voltage tester, take some things apart and look into the barn wiring.
220/221 is offline   Reply With Quote
Old 06-14-2009, 01:22 PM   #5
Thanks for the replies. I have just a little experience with electrical work.
The 2 wires to the barn is they way it has been for 20+ years may be more. I only replaced the cable from the breaker to the outside wires, as the old one, the sheath was worn off and bare wires exposed. Like I said I could have put the hot wire on the neutral wire that goes to the barn.
I check the barns panel. The bus bars are hot. I checked 2 receptacles, hot with tester in the hot side of outlet and one on neutral side, also ok when on hot side of receptacle and one in the ground. When tester is on ground and neutral, nothing.
I know the wire overhead from house to barn needs to be replaced, just dont have the time or money at this point.
Old 06-14-2009, 01:29 PM   #6
Well........keep you kids out of the barn because a funeral will be very expensive.
If polarity is right, you have an open neutral and a bootlegged ground somewhere.
Old 06-14-2009, 01:33 PM   #7
Well, the power is tuned off to the barn from the house panel.
Would you be as so kind to define an open neutral and a botlegged ground?
The barn panel has a wire going to a pipe driven in the ground, it is not up to code.
Old 06-14-2009, 02:43 PM   #8
DIYer
No, no, no.
Just because something works doesn't mean it's right. There's at least a dozen ways that electrical can be very wrong and unsafe and still work.
Never just guess and see if it works.
Gigs is offline   Reply With Quote
Old 06-14-2009, 02:56 PM   #9
DIYer
The ground rod won't trip the breaker because it's way too high resistance. It's basically only there for lightning and static protection, it doesn't serve any purpose otherwise.
So you have a two wire 120v circuit going out, no ground... Or do you have 220v going out there, no ground no neutral?
Either way, this is all a really bad idea. You need 4 wires to do this right, and 3 wires to even do it anywhere near safely.
Old 06-14-2009, 04:42 PM   #10
To explain it simply, the power comes to the barn on the hot and goes back on the neutral.
If the power is getting to the barn but not back to the source on the neutral, the electrons will take whatever path to ground that is available.
<<<<<<<<<<<<<<<<<<<<<<<<<<<<<<<<<<<<<<<...hot
b
a
r
n
>>>>>>>>>>>>>>>>>>>>>>>>( open )>>>>>>>>>>neutral
v
v
v
v
ground
A bootlegged ground is where the ground gets attached to the neutral in a recep, switch, panel or who knows where. It can be intentional or accidental.
Open neutral plus bootlegged ground equals current flowing thru metal parts that.
Old 06-14-2009, 06:34 PM   #11
Ok Thanks GUYS!
So to fix this, I should run 2 hots, a neutral, and a ground from my house panel, up and overhead, to the barn and down to a panel in the barn?
What size wire would you use, I think 50 amp is enough. Should I buy a new panel for the barn? Do I run 2 grounding rods for the barn too?
Thanks again
Old 06-14-2009, 06:53 PM   #12
Mystery of getting shocked on sbpnl.+Gfi n. trppng.
IMHO you [probably] reversed the connection on the GFCI receptacle! i.e. Line/Load, in addition to possibly having reversed the Hot/Neutral wires on the pull to the barn. The GFCI recept. should have tripped when you got shocked by touching the motor frame. Because you produced leakage current. But when you reverse the line/load terminals the outlet will work but will not provide protection, unless it's one of the later "lockout" versions!!!(smbol of confusion!) Don't Drink and Drive!!!
spark plug is offline   Reply With Quote
Old 06-14-2009, 09:08 PM   #13
DIYer
Ok Thanks GUYS!
Yes
How far is it? If it's like 100 feet then 6 gauge copper or 4 gauge aluminum SER cable should be OK.
We don't know what your existing panel looks like.
Two ground rods >6 feet apart is best.
Old 06-15-2009, 02:18 AM   #14
" Euro " electrician
frenchelectrican's Avatar
Originally Posted by Gigs View Post
How far is it? If it's like 100 feet then 6 gauge copper or 4 gauge aluminum SE cable should be OK.
Gigs ., Just give you a head up the SE is 3 conductor cable while SER is 4 conductor cable that is a crictal part you have to be carefull that all.
Now to OP
The distance between the house and barn if under 100 feet { 30Metre } then Gigs's suggest of conductor size is correct however becarefull if you going overhead or underground route there is three or more diffrent type you can use
For overhead use the quadplex overhead conductors.
For underground Direct burial use the URD quadplex or Mobile home feeder cable
For underground conduit use ., use the THHN/THWN conductors { they are dual rated }
Yeah for ground rods keep them apart 6 foot { 2 metre } apart and keep it out where rain water will get them.
{ you only need #6 (16mm˛) will do the task very well }
Merci,Marc
Old 06-15-2009, 07:52 AM   #15
DIYer
Oh, OK thanks.. I will edit my message so no one gets confused.
Adding a subpanel to a sub-panel and other questions CardinalPilot Electrical 14 03-30-2011 02:23 PM
Elec short causing A/C problems or A/C problems causing elec problems? Marlon Electrical 2 06-25-2008 02:04 PM
Another subpanel question:) primal65 Electrical 15 06-22-2008 09:43 AM
Reverse Polarity at the Subpanel adm060306 Electrical 14 07-09-2007 12:58 PM