10/3 UF is about $1 per per .. ( that would be 4 wires )
#10 Thhn/thwn is about .38 per foot x 4 = 1.52 per foot PLUS the conduit ..
that why some use UF ....in the condiut ...
Philadelphia Master Electrician-Generac Dealer
Philly Master is offline   Reply With Quote
The Following User Says Thank You to Philly Master For This Useful Post:
shedwire (11-14-2013)
Old 11-30-2013, 01:28 AM   #17
I hope everyone had a filling Thanksgiving.
Looking back and the older post from Philly Master says “10 wire = 30 amp breaker”.
Should I go with the 30 amp breaker instead of 20 amp since I will use a #10?
(Approximate values for shed: 2 circuits; 1500 watts and 1360 watts = 2860 total watts)
Thank you
shedwire is offline   Reply With Quote
Old 11-30-2013, 06:30 PM   #18
Thank you
there isn't anything (typically) wrong with running a larger conductor size than that required by the rating of the circuit breaker. a #10 on a 20-amp breaker is fine. but if you are already running #10, why not take full advantage of its 30 amp capabilities and get a 30 amp breaker? why leave 10 amps "on the table"?