Sharing Neutrals On The Same Phase - Electrical - Page 2 - DIY Chatroom Home Improvement Forum
Old 10-30-2009, 03:37 PM   #16
Originally Posted by Stubbie View Post
Habits are hard to break but I'm finding it less taxing of my time to look in on the forum and respond to something that I feel I may add some drawings that will help what all you guys explain so well.
...thanks for the excellent explanation and drawings as usual!
Willis
williswires is offline   Reply With Quote
Old 10-30-2009, 03:50 PM   #17
UAW SKILLED TRADES
Stubbie's Avatar
Rewards Points: 2,652
Originally Posted by electro View Post
" "Unbalanced" isn't the correct term " I thought about that a little while after I posted , That term would refer to the current carrying conductors .
Thanks guys .
It's good to have conformation that I'm on the right page .
Electro
The grounded leg or neutral is a current carrying conductor just as the hot wires. Either can knock the morning dew off you.....
That term unbalanced is actually how most electrical textbooks explain what we have been discussing here on this thread. Example from a text book....."the shared neutral of a multi-wire branch circuit carries the unbalanced current while the balanced current cancels" another more confusing way to say it carries the difference.....
" One nice thing about the NEC articles ... you have lots of choices"
Stubbie
Old 10-30-2009, 03:51 PM   #18
zpm
yeah, right
Originally Posted by busman View Post
Yeah, but who can find the code violation. It's a killer to find.
One way to look at it being a violation is that the definition of a MWBC is:
Branch Circuit, Multiwire.
A branch circuit that consists
of two or more ungrounded conductors that have a voltage
between them, and a grounded conductor that has equal
voltage between it and each ungrounded conductor of the
circuit and that is connected to the neutral or grounded
conductor of the system.
If there are two ungrounded (hot) conductors on the same leg, there's no "voltage between them". That means its not a MWBC and you can't use any of the MWBC code sections.
Honey, does this tool belt make me look FAT?
zpm is offline   Reply With Quote
Old 10-30-2009, 03:55 PM   #19
zpm
yeah, right
Originally Posted by Scuba_Dave View Post
In addition under NEC 2008 you have to use a 240v breaker for a MWBC, so sharing across the same buss is not possible
That's the easy way to do it. But single pole breakers with a handle tie are also allowed. A MWBC needs a common disconnect, not a common trip. 210.4(B)
Old 08-11-2010, 05:48 PM   #20
what about 3 ph *edited*
Personal attacks of any kind will not be tolerated
Moderator
jcollins is offline   Reply With Quote
Old 08-11-2010, 06:14 PM   #21
Electrical Contractor
jbfan's Avatar
Rewards Points: 224
Originally Posted by jcollins View Post
what about 3 ph
What about it.
It also needs a common disconnect.
Old 08-11-2010, 06:17 PM   #22
Electrician
Proby's Avatar
Originally Posted by jbfan View Post
What about it.
Which is absolutely HORRIBLE.
Anything fun is either illegal, immoral, or fattening.
Proby is offline   Reply With Quote
Old 08-11-2010, 10:52 PM   #23
Rewards Points: 1,440
On a three phase system, one neutral can be shared by three hot wires, one from each of the phases. A MWBC of this kind would have three breakers with handles tied together.
With a 3 phase system, and an MWBC, the math for computing the current on the neutral is somewhat more complicated.
Old 08-12-2010, 05:07 AM   #24
Rewards Points: 726
Originally Posted by 220/221 View Post
Multi wire branch circuit.
If you have 20 amps from one hot and 20 amps from another hot, you have 40 amps on the neutral if they are on the same phase.
If they are on different phases, they use the neutral at different intervals.
Actually, they don't use the neutral at all, if they are balanced loads. Draw a circuit diagram with two equal resistors on a split phase (single phase) circuit. You'll see that with phasor voltages, the voltage at the center between the two resistors is zero. Zero volts to ground equals zero current flow in the neutral. You could disconnect the neutral on a balanced circuit with no effect.
Mark
busman is offline   Reply With Quote
Old 08-12-2010, 06:14 AM   #25
Master Electrician
Rewards Points: 3,746
Mark
No effect other than to destroy most 120 volt equipment on the circuit.
brric is offline   Reply With Quote
Old 08-12-2010, 07:09 AM   #26
jbfan's Avatar
Rewards Points: 224
Been there, done that.
Disconnected a neutral and watch magic smoke rise from several computors!
Old 08-12-2010, 07:24 AM   #27
Rewards Points: 726
Only if the load isn't balanced. If the loads are the same, there will be no damage (in fact no effect at all) from disconnecting a neutral.
Mark
Old 08-12-2010, 08:31 AM   #28
Electrician
Proby's Avatar
Not if it's a balanced load.
Old 08-12-2010, 09:12 AM   #29
I=E/R
a7ecorsair's Avatar
It is surprising how confusing this topic is and it has been discussed several times in various ways. Without the neutral, the MWBC is nothing but a 240V circuit with two loads in series. The center tapped neutral forces this to two "constant voltage" circuits. Proper application of Ohms Law will explain everything.
a7ecorsair is offline   Reply With Quote
Old 08-12-2010, 01:33 PM   #30
UAW SKILLED TRADES
Stubbie's Avatar
It is surprising how confusing this topic is ....
Why do you find it surprising?
Stubbie
Want to add a single phase Subpanel to three Phase Main meglomachinist Electrical 19 09-10-2009 04:46 PM
How to power a 120/240 volt 3 phase oven in a building with 120/240 volt single phase wantsomegetsome Electrical 9 05-04-2009 11:49 AM
120/208/1 phase wiring questions JohnJon Electrical 11 09-01-2008 12:28 AM
3 phase electricity J187 Electrical 11 10-26-2006 02:40 PM