Shared Neutral - Electrical - DIY Chatroom Home Improvement Forum
Old 07-15-2012, 01:10 PM   #1
Rewards Points: 162
Shared Neutral
I'm not fully understanding what's allowed for a shared neutral and ground. I have 10/3 UF running underground from the garage to a pool outlet and also a shed. The red wire isn't being used. The circuit is on a timer, so I can't use the shed unless the pool pump is running.
Can I make the red wire the shed's power, the black wire the pool's outlet, and share the neutral and ground between them? My understanding is this would be allowed only if each circuit was protected at 15 amps, so the neutral would never exceed 30 amps.
matt151617 is offline   Reply With Quote
Old 07-15-2012, 01:28 PM   #2
Master Electrician
I believe you would have to have the wires on seperate legs in the panel. This would make it so the unbalanced load flows back on the neutral and would never exceed 15a not 30a.
Sarcasm is my friend
I'm here to learn too, i do mostly commercial/industrial/new construction and this place is a great way to pick up tips on residential from some good electrical minds. Excuse the spelling, my phone has a mind of it's own.
andrew79 is offline   Reply With Quote
Old 07-15-2012, 01:34 PM   #3
Licensed Electrician
k_buz's Avatar
Rewards Points: 2,006
Pool pumps cannot be wired with UF due to the requirement of an insulated ground.
Old 07-15-2012, 05:08 PM   #4
Rewards Points: 1,548
When you have red, black, white (and ground) in a cable you can share the neutral (white) when red and black are on opposite sides of a 120/240 volt circuit (240 volts between the two) and then for 10 gauge wire you can have 30 amps on each. This produces two allotments of 120 volts at 30 amps or one allotment of 240 volts at 30 amps or some combination in between. The actual current on the neutral will range from 0 to 30 amps as the difference between the amperes on the red and on the black.
Should red and black of a cable with one white wire be on the same side of the 120/240 volt line they must both be on the same circuit, i.e. on the same single breaker supplying 120 volts (up to 30 amps for 10 gauge). This latter might be the case if black is unswitched and red is switched at a box downstream of the panel (a cable without the red wire goes between the switch box and the panel). Note that the maximum amperage allowed to reach ordinary switches and receptacles and light fixtures is 20 amps. A (10 gauge) circuit actually breakered at 30 amps must go to a subpanel first before any of the aforementioned devices can be wired (downstream of 15 or 20 amp "sub-branch circuit" breakers).
Ten gauge may be used (and needed) for a 20 amp circuit if the distance from main panel to receptacle is great, say more than about 150 feet.
Old 07-16-2012, 05:52 AM   #5
Rewards Points: 162
So as long as I put the 2 separate breakers on top of each other on the panel, they can be split?
Old 07-16-2012, 05:55 AM   #6
E2 Electrician
stickboy1375's Avatar
Rewards Points: 2,970
Yes, but the maximum breaker you could use is a 20 amp.
Old 07-16-2012, 06:35 AM   #7
The 20 amp breaker limit occurs because of the wire size (not relevnt in the OP's original question) or there are/will be devices intended for circuits with no more than 20 amps with no subpanel breaker in between.
Not because the neutral is shared.
The Following User Says Thank You to AllanJ For This Useful Post:
stickboy1375 (07-16-2012)
Knob and Tube shared neutral planes Electrical 8 06-26-2012 04:00 PM
Shared Neutral BobSmitt Electrical 22 09-21-2011 02:26 PM
breakers with multi wire branch circuit (shared neutral) corman Electrical 0 09-10-2011 11:52 PM
Sharing Neutrals on the same phase electro Electrical 30 08-12-2010 02:10 PM
Ground rod or not? brotherman Electrical 30 07-15-2008 04:58 PM