so the breakers need to match the panel as far as manufactures go?
ramick is offline   Reply With Quote
Old 11-14-2012, 06:48 PM   #17
Pure Genius
Rewards Points: 150
Yes. Some breakers will fit in other panels but they wont make good contact. Ive seen busses melt from the wrong breaker being installed.
Dierte is offline   Reply With Quote
Old 11-14-2012, 06:53 PM   #18
OK I will have a look.
Old 11-14-2012, 09:45 PM   #19
Rewards Points: 758
Is this a detached garage? If so, you need to add ground rods (2).
In the panel, you also need to separate the neutrals and grounds, that's why the 4 wire feed. You'll need to add a ground bus and make sure the neutral bus is not bonded to the panel.
AandPDan is offline   Reply With Quote