Rural (farm) location. The current service disconnect resides immediately below the meter box on a pole. It is the plan to upgrade the service capacity to 125 amps.
Must the service disconnect reside immediately after (below) the meter?
jlmran is offline   Reply With Quote
Old 12-29-2012, 09:57 PM   #2
Electrical Contractor
jbfan's Avatar
Rewards Points: 386
It can be put on the house/shed/or what ever you are powering.
Old 12-29-2012, 10:07 PM   #3
Rewards Points: 506
From the existing service disconnect on the pole, overhead feeders go to a house, a barn, and a well pump. A new detached garage/shop is being built, and the plan is to remove the old DC and place a new service DC in the new panel, inside the new garage/shop. The new garage/shop is located very near the pole. Any problems with this plan?
Old 12-30-2012, 07:16 AM   #4
Licensed Electrician
k_buz's Avatar
Rewards Points: 2,006
Are the existing feeders being moved to the new shop as well?
Old 12-30-2012, 07:23 AM   #5
Rewards Points: 506
Yes, and each feeder will have its own circuit breaker.
They won't be really moved...but their point of origination will be extended into the panel.
Old 12-30-2012, 07:35 AM   #6
k_buz's Avatar
I can't see a problem with what you want to do either. I don't know if your location (farm) will require a permit, but you will want to be down at least 3' as I assume the feeders will be under an area that is drivable.
My personal opinion is that if the existing pole is staying, I would keep a panel at that pole, that way, the underground feeders are protected.
Old 12-30-2012, 07:43 AM   #7
Rewards Points: 506
Deleted
Old 12-30-2012, 07:48 AM   #8
Rewards Points: 506
Our Permits and inspections are nothing more than money exchanges, and they are required.
All feeders are overhead. So my plan was to extend the service into the new panel through pipe, then feed back out to the pole through the pipe. The pole will still require some type of junction box for the feeder splices, since everything on the existing pole will remain (except service disconnect).
Old 12-30-2012, 07:50 AM   #9
Rewards Points: 1,494
I don't know the exact requirements but I believe that the requirements for the service entrance conductors or cable are different upstream of the disconnect compared with downstream. So by moving the service disconnect location from the pole to a building, you may need to run different kinds or sizes of conductors overhead or underground.
There is no overcurrent protection other than (probably) the pole transformer primary fuse for the wiring including the service conductors upstream of your service disconnect.
No changes would be needed for the overhead lines from the yard pole to the other buildings, now fed from a breaker in the main building's panel.
Here, no, but the reason this question pops up is that, in a typical home installation with the meter on an outside wall and the panel on an inside wall (in the basement?), there is a limit to the length of the pre-disconnect service cable in the house (again, no overcurrent protection other than back at the pole transformer) connecting the two.
Old 12-30-2012, 08:01 AM   #10
k_buz's Avatar
I will look it up, but I'm not sure you can run unfused and fused feeders in the same raceway.
Old 12-30-2012, 08:24 AM   #11
k_buz's Avatar
After thinking this through, I wouldn't do what you are planning. You are adding unnecessary cost, extra splices, and unfused feeders. If you are going to have a JBox on the pole anyway, I think I would install a 3R panel on that pole.
What size is the service going to be? Single or 3 phase?
Old 12-30-2012, 08:27 AM   #12
Rewards Points: 506
Perfect...thanks.
Old 12-30-2012, 10:20 PM   #13
" Euro " electrician
frenchelectrican's Avatar
It used to be legit before not anymore only exsting installment can stay but anytime the service will be upgraded then the fused and unfused conductors have to be seperated.
The other issue what I heard that many POCO is getting strict with their pole they don't really want anything on it beside the meter that it.
k_buz., Just look up your POCO regulation book on farmstead set up they will mention that.
Merci,
Marc
Old 12-30-2012, 11:19 PM   #14
Rewards Points: 506
125 amp single phase.
I agree that if a jbox on the pole is needed anyway, why not make it a panel? Thanks.
Old 12-31-2012, 06:10 AM   #15
k_buz's Avatar
125A for a house, a barn, well pump, and a new shop? Seems awful small.
Juggling power during service upgrade. WillK Electrical 2 05-04-2011 05:40 AM
missing service disconnect breaker willywainwright Electrical 2 04-05-2011 01:47 PM
New service Help (Meter can/ service mast Conduit help) cwolford Electrical 13 03-26-2011 07:55 PM
"Moving" service entrance WillK Electrical 4 09-29-2010 01:04 PM
New Service msagers Electrical 1 02-13-2008 02:08 PM