My service panel has a new ground rod located right next to the panel. It uses 4 gauge wire (100a panel). I installed the new rod because I thought the existing rod was too far away from the panel (about 40').
My question has to do with a coax splitter where the line comes in from the pole into my house, and is split to the modem & cable box. There is a ground screw on the splitter, so it appears it is designed to take a ground wire. The splitter & coax service line is located about 25' from the main service panel and new ground rod.
The old ground rod is about 15' from the splitter.
I've read that you should never use two ground rods, but would this include having the panel on one rod, and the splitter on a different rod? Or should I just run a 25' section of copper grounding wire and tie into the service panel grounding rod?
Thanks in advance.
sheslostcontrol is offline   Reply With Quote
Old 12-31-2011, 01:09 PM   #2
MarginallyQualified
Rewards Points: 2,464
Attach the splitter to the bare ground wire (#12 is OK)...
or to the old rod if that is closer.
I've read that you should never use two ground rods...
You read wrong. There are all sorts of reasons to use two rods.
Some are even good reasons.
BTW... if you get a wild hair and feel compelled to run a wire between the two ground rods you have... don't use anything less than a #6 wire.
hth
Old 12-31-2011, 01:16 PM   #3
Julius793's Avatar
Thanks in advance.
Thats not true you can use as many ground rods as you want
Electricity will kill you if you give it a chance
Julius793 is offline   Reply With Quote
Old 12-31-2011, 01:24 PM   #4
Licensed electrician
Rewards Points: 1,020
The two rods do need to be connected together.
Code05 (12-31-2011)
Old 12-31-2011, 01:34 PM   #5
Semi-Pro Electro-Geek
Rewards Points: 2,858
Hopefully he does, because it's required. No matter how many ground rods are installed (and usually two are required), they all MUST be connected together and bonded to the system neutral conductor.
Installing extra ground rods and connecting things to them without bonding them to the system is not code compliant, and can be more dangerous than having no ground rod under certain fault conditions.
mpoulton is offline   Reply With Quote
The Following 2 Users Say Thank You to mpoulton For This Useful Post:
Code05 (12-31-2011), Jim Port (12-31-2011)
Old 12-31-2011, 01:50 PM   #6
MarginallyQualified
That is plainly untrue. I get your point but it's too simplistic.
There are millions of old services functioning perfectly well without the second rod.
Some jurisdictions (and contractors) have gotten into the practice of accepting two rods rather than going through the trouble of testing the impedance or resistance with one rod... and/or the metal water pipe issues etc (250.53, .56) (Not that the second rod does anything wrt improving inadequate impedance.
Er no, not quite. More than two is never required...
but on jobs where the second rod is called for.... is it ever set 40 feet apart from the first? No.
Old 12-31-2011, 01:55 PM   #7
Rewards Points: 87
Hi all,
I'm a belt-and-suspenders kind of a guy. I would bond old rod to new with 4 ga. copper or better, and bond the splitter to the old one with 8 ga. copper. (IIRC: NEC requires either 8 ga. aluminum or 10 ga. copper for antenna grounding. So I go it one better and use 8 ga. copper.)
Yes. Two separate grounding systems is regarded as a Bad Thing, by many. (May even be against code? Dunno.) Two reasons: 1. Not all grounds are created equal. You can actually get voltage differentials between different grounds, and 2. If your service ground degrades, then the path to the other ground may see current flow for which it's not designed.
I figure bonding them, as I would do, makes both those problems go away.
Properly bonded together: More ground rods are better than fewer. (Assuming they're all effective, which, depending upon a variety of factors, isn't necessarily a given.)
Jim
More Power! is offline   Reply With Quote
Old 12-31-2011, 02:22 PM   #8
Article 250 of the NEC clearly requires any and all grounding electrodes to be bonded together. If there are 2 rods they need to be connected together. You cannot use one for the service and one for the cable and/or phone.
The Following 5 Users Say Thank You to Jim Port For This Useful Post:
Code05 (12-31-2011), gregzoll (12-31-2011), More Power! (12-31-2011), mpoulton (12-31-2011), SD515 (01-01-2012)
Old 12-31-2011, 02:35 PM   #9
Julius793's Avatar
Does nec require grounding coax?
Old 12-31-2011, 02:41 PM   #10
Rewards Points: 87
Clarify, please. "Coax" can mean anything from cable TV, to outside antenna, to the coax used to connect together various home theater components.
That last instance (HT components): No. Outside antenna: Definitely yes, along with a lightning arrestor. Cable TV: I honestly do not know. (My cable company installer did, however.)
Jim
Old 12-31-2011, 02:47 PM   #11
Rewards Points: 150
This opens another can of worms. Fixing the original issue by tying old and new rods together with #4 copper is easy enough (except for the cost of the wire ugh).
I have a detached garage with its own service panel and separate power feed from the street. It has its own ground rod and was originally not connected with the house in any way. Then I wanted to extend coax, cat5 and security system wiring to the detached garage, which I did using appropriate underground cable and 4" bury-able conduit.
Sounds like I have a new problem I didn't see before. That coax & ethernet wire creates a path for electricity to follow, if things were to degrade with the right conditions.
Pulling #4 copper wire through 50' of conduit with two 45s is going to be pure hell. That is if I don't damage the existing wiring (one of the security feeds is 24 gauge).
Is it OK to bury ground wire direct in the dirt (between the house & garage), or does that negate the purpose of having a single ground rod?
Old 12-31-2011, 02:53 PM   #12
Julius793's Avatar
Jim
Well what I was trying to get at is assuming what the OP wants to ground is not regulated by the nec, then he can connect it to a separate grounding rod.
Old 12-31-2011, 03:03 PM   #13
You should not have both 120/240 and security wiring in the same conduit.
The grounding conductor does not have to be solid. In fact larger than #8 is stranded anyway. The bare or green solid is used outside of a conduit due to its lack of flexibility.
Old 12-31-2011, 03:16 PM   #14
Rewards Points: 87
No, he cannot. The shield from that coax is going to be connected to the chassis ground on the cable modem and converter boxes, thus to ground (and most likely neutral, btw) on the inside wiring. This is precisely the problem that the NEC seeks to address by prohibiting separate grounding systems.
Jim
Old 12-31-2011, 03:24 PM   #15
Julius793's Avatar
Jim
Ok I'll take your word for it cuz its out of my field
Cable & separate ground wire in conduit? shadetree Electrical 3 12-17-2011 09:19 PM
voltage on ground wire - multiple ground problem? Thaiman Electrical 14 04-02-2011 12:49 PM
Attach #4 Copper to Neutral/ Ground Lug Sierevello Electrical 3 01-29-2011 02:04 AM
Electrical Ground Problem cabinetman Electrical 15 01-28-2010 05:55 PM