Old 12-04-2008, 08:25 AM   #1
A "Handy Husband"
rjniles's Avatar
Second circuit to detached garage?
I have a detached garage (workshop) with 1 20amp circuit. I use a small compressor and when it starts my Fluor. lights dim and flicker( irritating). Building is 40 feet from house (maybe 100 feet from CB panel). I would like to add a second 20 amp circuit to run my compressor and table saw. I think this will stop my lights problem. Question is my plan code compliant? Can I have 2 seperate circuits in my detached building without adding a sub-panel?
rjniles is offline   Reply With Quote
Old 12-04-2008, 09:35 AM   #2
Licensed Pro
Not code compliant. Your options are to run a larger 4-wire UF cable and add a subpanel or run a 12/3UF and have a multiwire circuit. I would opt for the subpanel.
Old 12-04-2008, 09:11 PM   #3
I second the sub panel. It will give you the ability to add more circuits down the road if you wish.
Plumbvoltage is offline   Reply With Quote
Old 12-04-2008, 10:33 PM   #4
Electrician
One feeder per structure, but how is the gargage fed now? Direct buried wire or conduit?
chris75 is offline   Reply With Quote
Old 12-05-2008, 07:23 AM   #5
A "Handy Husband"
rjniles's Avatar
The existing wire is direct buried UF; so I will be digging for any option. Why is there a 1 feeder per building limit? Is it a safety issue?
Old 12-06-2008, 01:03 PM   #6
J. V.'s Avatar
NEC Art. 225.30 makes this rule. The reason is for safety. Lets say you have two circuits feeding a building and you turn one off. But do not realize there is another power source that is still on. You still have power in the building. You want to kill all power with one breaker. So a feeder or multiwire branch circuit would be the choice.
Mold in detached garage jkrodger Building & Construction 15 05-01-2009 02:46 PM
Light Switch to Detached Garage - Grounding Issue smitty286 Electrical 1 10-22-2008 01:17 PM
GFCI in detached garage question WShawn Electrical 2 08-02-2008 04:27 PM
Grounding for detached all-metal garage geeswanie Electrical 3 07-03-2008 08:31 AM
Circuit Problems - Garage DisturbedPanda Electrical 9 08-03-2007 10:23 PM