Is This Safe (GFCI In Old Home) - Electrical - DIY Chatroom Home Improvement Forum
Old 02-24-2012, 04:14 AM   #1
Is this safe (GFCI in old home)
Ok so I have 4 wires in my box... 2 white 2 black. no ground but it is a metal box that I think is grounded. Anyways, I figured out which set was line and which set was load and hooked up the 4 wire but left ground alone(nothing hooked to the ground screw on the GFCI)
Am I getting any kind of actual protection? Am I gonna burn my house down? Anything else I need to know?
oopsimscrewed is offline   Reply With Quote
Old 02-24-2012, 04:38 AM   #2
That's the way to do it when no ground wire available.
Actually if you get the line and load mixed the GFI won't reset.
Make sure you test it with the button.
It will work as intended without the ground wire.
The problem is that any fault current doesn't have an easy path to ground. It will get there. Hopefully not hurting anything.
jammin06 is offline   Reply With Quote
Old 02-24-2012, 07:32 AM   #3
Licensed electrician
Rewards Points: 1,764
There is no guarantee that the metal box is grounded. The wiring method would need to supply a grounding means before the box is grounded. Otherwise it would just be floating.
Old 02-24-2012, 07:38 AM   #4
Rewards Points: 3,256
But it is the recommended way for some protection in a groundless system....no?
zappa is offline   Reply With Quote
Old 02-24-2012, 07:53 AM   #5
UAW SKILLED TRADES
Stubbie's Avatar
Rewards Points: 2,652
YEP
Because there is no ground the gfci will protect you from electrocution but not shock. By that I mean if there was a ground wire installed and an effective ground fault path established any fault to ground would trip a breaker. This would protect you from both shock and electrocution as the branch circuit would be de-energized. If however no ground is present and only a gfci then the gfci would sense any milliamps of leakage current between the hot and neutral. So if a ground fault was present that would not clear due to the absence of a ground fault path .. and you touched any bonded metal that was energized you might receive a slight shock just before the gfci tripped. The important thing is you won't receive a fatal shock.
Just remember that a gfci breaker protects the entire circuit and a gfci receptacle only protects load side of the receptacle.
" One nice thing about the NEC articles ... you have lots of choices"
Stubbie
Can you test a non GFCI plug with a GFCI tester? DIYguy2000 Electrical 3 01-16-2012 06:49 AM
GFCI troubleshooting XwpisONOMA Electrical 20 11-13-2011 05:19 PM
Installing GFCI outlets in old home surdules Electrical 2 10-20-2010 10:22 AM
GFCI intermittent nuisance trips jejm1975 Electrical 43 09-07-2008 09:18 AM
Freestanding/portable safe home heaters?? sugarmama HVAC 5 10-30-2007 08:23 PM