Roundeye 09-17-2011 04:36 PM
Ive got an electric wall heater that's 120v and pulls 12.5 amps. What's the easiest way to wire it up? Can I run it off of an existing breaker or can I tie in to other wires near by?
darren 09-17-2011 04:43 PM
With that type of load you will need a dedicated circuit. In Canada you could get away with #14 wire and a 20A breaker, with that said I would still run #12 and a 20A breaker if it was me.
Jim Port 09-17-2011 04:57 PM
You would need a dedicated circuit under the NEC. You cannot add this to a circuit that would also have cord and plug connected loads since it is over 1/2 of the circuit rating even for a 20 amp circuit.