Old 07-12-2008, 12:23 AM   #46
Power Gen/RS Engineer
running wires in a conduit
Originally Posted by analogmusicman View Post
I'm baaaaak! bet y'all thought I left the country,huh? (some wish I HAD!)
anyway,I've been reading that a kitchen MUST have a 20A circuit for the fridge,micro,disposer. well,outside of that big 50A circuit I'm running for the range, only 15A circuits are available so, I'm wondering if that 3/4 EMT will hold a couple more wires for a 20A circuit. total wires in the 3/4 would be 3 #6,1 #8 and 2 #12 (I;m assuming #12 for a 20A circuit) so what do you think?
BTW: getting close,the electrician comes over on Mon. to upgrade the panel to 150A then I'll be able to start putting up conduit and pulling wires...my wife can't wait!
tnx,
Put in a length of 1" emt. Just my gut (I'm not consulting tables here). If you're gonna run pipe, bigger is always better. And don't go by the NEC tables. Most electricians will brain any designer that takes it to the limit specified as being "acceptable"
Just my opinion,
Jimmy
The very existence of flamethrowers proves that some time, somewhere, someone said to themselves,"You know, I want to set those people over there on fire, but I'm just not close enough to get the job done." - George Carlin
BigJimmy is offline   Reply With Quote
Old 07-12-2008, 09:31 AM   #47
Licensed Electrician
jrclen's Avatar
Assuming THWN/THHN you are over the limit for 3/4 EMT. Per Chap 9 NEC.
John
jrclen is offline   Reply With Quote
Old 07-12-2008, 02:12 PM   #48
analogmusicman's Avatar
according to the Belden chart, I'm on the "hairy edge"! total area of 3/4 emt is .21331 sq. in. and my wires come in at .2144 sq. in. (for a 40% fill) any leeway here or should I just "bite the bullet" and go to 1" emt?
tnx,
analogmusicman is offline   Reply With Quote
Old 07-12-2008, 04:13 PM   #49
tnx,
Analog-
Go with 1" regardless. You'll be happy you did. Most electricians will be happy to tell you that the fill tables indicate what is allowed but not necessarily practical from an install/pulling point of view. For instance, per Chapter 9 annex C, you can install up to 9 #12 THHN wires in a 1/2" stick of emt but it'd be no picnic.
Old 07-12-2008, 10:02 PM   #50
well,ok, "BIG",you convinced me,darn it! this definitely throws a "monkey wrench" into the works since 1" emt and fittings are double over 3/4 inch and that emt looks tougher to bend. the electrician coming over on mon. to upgrade my panel just might be getting some more work!
tnx,
Old 07-13-2008, 09:49 AM   #51
jrclen's Avatar
tnx,
My numbers come to .213 and .2153. These are from the NEC book. And that is what the electrical inspector will use. This seems like a very small thing. .002 doesn't sound like enough to make a difference. But what if you install the whole thing and the inspector red tags it and tells you to increase the size of the conduit? I would go with the 1" conduit. Or use EMT for the entire run and eliminate the #8 ground. But it's your call.
John
Conduit Fill & Ampacity capndave Electrical 37 03-26-2008 03:16 PM
How many wires in 1/2" conduit? alvanos Electrical 17 02-26-2008 04:37 PM
Running wires in corners mt232 Electrical 13 04-10-2007 10:21 PM
Running wires mt232 Electrical 4 03-22-2007 09:02 AM
Running Conduit in new basement framed walls tben Electrical 3 12-11-2004 12:14 AM