Running Wire For Well Pump - Electrical - DIY Chatroom Home Improvement Forum
Old 03-08-2012, 02:00 PM   #1
Question
Running wire for well pump
Just installed a well and need to run electrical power out to it. The run is about 100 ft, and the pump requires 240 and a 30 amp breaker.
I plan to later install booster pump and maybe a light after I build the pump house.
So here are my questions.
First from what I can tell, I need 8 gauge wire. (right, wrong?)
and since I am running 240 volts, 3 wires (2 hot + a return).
Since I might in the future need a 120V source out there do I need to run 4 conductor cable (8/3) or can I just split off a branch.
Also I am confused about the cable I need. Does 240 need 3 wires or 4?
Also since underground cable is about 2x the price, I was planning on using PVC and installing regular cable. Thoughts?
matkyne is offline   Reply With Quote
Old 03-08-2012, 02:02 PM   #2
Electrical Contractor
rrolleston's Avatar
Rewards Points: 1,012
Send a message via AIM to rrolleston Send a message via Yahoo to rrolleston
How long of a run total with the wire going down the well?
With Electricity there is the right way to do it and the dead way. Just because it works does not make it safe.
rrolleston is online now   Reply With Quote
Old 03-08-2012, 02:04 PM   #3
The well is about 900 feet deep. it is wire with 3 10 Gauge wires.
Old 03-08-2012, 02:14 PM   #4
rrolleston's Avatar
If you are planning on running a booster pump and some 120v stuff out there maybe you could add a 50 amp sub panel out there with some 6-3 w ground wire and you would have power for both the pump, booster pump and some 120v outlets without running all separate lines. 6-3 wire panel couple ground rods and ground wire.
I have seen many people put a shed around the well. Having a dry place to do well maintenance and an option to run a winch to help pull the pump if you need to replace or repair the pump in the future would be well worth it.
The Following User Says Thank You to rrolleston For This Useful Post:
matkyne (03-08-2012)
Old 03-08-2012, 02:18 PM   #5
So at 30A for a <5% voltage drop you need <.05 x 240v/30A = <0.4 ohm. For a 2000' loop distance you need a wire with <0.4/2000' = <0.2 ohms/1000'.
#3 copper?
Old 03-08-2012, 02:25 PM   #6
3 gauge wire seems excessive.
Old 03-08-2012, 04:28 PM   #7
To me, too.
Post your recommendation along with calcs.
Old 03-08-2012, 04:41 PM   #8
Licensed electrician
Rewards Points: 1,794
You cannot run indoor rated wire or cable inside a conduit that is outdoors or buried.
Straight 240 only requires 2 hot conductor and a ground.
If you are going to add other circuits you will need to run a feeder and add a subpanel. This would require a 4 wire feeder.
zappa (03-08-2012)
Old 03-09-2012, 12:49 AM   #9
" Euro " electrician
frenchelectrican's Avatar
First thing first.,
The word 240 volt 30 amp for pump motour that means really nothing to me at all due we will need to know excat number like how many HP the motour itself that will make the differnce on sizing the conductor for the well motour.
Second thing the conductor size from your main panel to subpanel at the pump house if you want 40 amp circuit I can able tell you what size but need to know the distance from main panel to the pump house or at well head location is.
Third thing you can not run NM cable in conduit for underground useage it is not legal per NEC code so only way you can do this is use the Direct burial cable ( UF cable ) or run in PVC conduit with THHN/THWN conductors those two items are approved for underground runs.
Now next thing is sencie you mention light and couple other things so you will have to bring out 4 conductor not three conductor.
For the pressure switch will be at the well head or in the house that will make the differnce.
I know you mention 900 feet I have simauir depth well in Wisconsin but the pump itself is only down about 500 feet so I do not have to use seriously oversized conductor ( due I did have 480 volts triphase pump motour there )
Merci,
Marc
Old 03-09-2012, 10:31 AM   #10
And maybe somebody makes a pump motor with a long driveshaft that hooks to a much deeper pump. Copper costs.
Old 03-09-2012, 08:58 PM   #11
Not for small well pumps. the larger one do have jackshaft set up so the motour stay at the top.
Merci,
Marc
Tags
240 volt , pump , water
Sump Pump Questions henlij Plumbing 22 03-16-2015 10:00 PM
Breakers, wire size and new heat pump ACR_SCOUT Electrical 21 01-29-2012 02:25 PM
Running wire to garage,HELP!! jukebox64 Electrical 4 03-17-2011 06:36 PM
Adding ground in old home ChaosTheory Electrical 6 06-16-2010 04:02 PM
wire running question ponch37300 Electrical 4 04-21-2009 03:58 PM