I am running 4 wires along the house sill plate new construction. Is this to code? Can I staple the wires to the sill plate and the rim joists? Also for new construction kitchen receptacles can I install non-gfci if the circuit will be on a gfci breaker?will the inspector approve?
RISurfer is offline   Reply With Quote
Old 08-01-2012, 08:33 AM   #2
Rewards Points: 13,266
Why would you not run the wires through a drilled hole in the floor joist? That way the wires would not be in the way later when someone wanted to finish the basement.
Old 08-01-2012, 10:35 AM   #3
JOATMON
ddawg16's Avatar
Rewards Points: 1,116
I believe per code, if the wire is running perpendicular to a joist, you have to drill a hole in the joist to run the wire.
Regardless..I think Joe is right....drill some holes and get those wires up out of the way. You want them at least 1.5" inboard to that it's unlikely a nail or screw will hit it.
On the outlets....yes, you can wire a TR outlet off the load side of a GFIC. It will be just as protected as the GFIC is.
Old 08-01-2012, 10:54 AM   #4
Master Electrician
He asked of he could use a gfci breaker. Yes you can. Makes no difference if you use a breaker or plug. Needs to be 20a though.
Sarcasm is my friend
I'm here to learn too, i do mostly commercial/industrial/new construction and this place is a great way to pick up tips on residential from some good electrical minds. Excuse the spelling, my phone has a mind of it's own.
andrew79 is offline   Reply With Quote
Old 08-01-2012, 12:22 PM   #5
Rewards Points: 3,130
Actually, for the kitchen he'll need two of them.
Old 08-01-2012, 12:42 PM   #6
I am helping the electrician do some of the work such as running the wires. He told me to run the wires along the sill plate on top of the concrete walls and then run them in to the stud bays. He didn't want me to run the wires through the floor joists. I figured this was one way of doing it.
Old 08-01-2012, 01:48 PM   #7
Is it faster to not have to drill the holes, yes.
Is someone going to have to go back and rerun the wires or add shims later if you do not drill the holes, most likely if you finish the basement.
Old 08-01-2012, 02:01 PM   #8
Rewards Points: 2,516
Exposed "romex" smaller than 8AWG running at angles with joists in unfinished basements and crawl spaces must either be run thru bored holes in the joists or on running boards. 334.15C
hammerlane is offline   Reply With Quote
Old 08-01-2012, 02:58 PM   #9
I'm using 14/2 and 12/2 should I bore holes through all the joists? Right now the wire runs parallel with the sill and adjacent to the joists.
Old 08-01-2012, 03:23 PM   #10
Lic Electrical Inspector
electures's Avatar
Rewards Points: 1,108
If you follow the letter of the code. No. However, for the 36+ years I have been wiring houses, it is commonly done. Just keep the wires up against the sill. As an inspector, I don't have a problem with it either. You may want to ask your local EI.
If you install GFI breakers, GFI receptacles are not necessary. You'll just have to run back to the panel everytime one trips.
All responses based on the 2011 NEC.
If you live in New Jersey click here. All other states click here.
Please check with local, county and state officials as laws may vary.
Sizing motors here. Online motor calculator here. Online calculators here.
electures is offline   Reply With Quote
Old 08-01-2012, 04:59 PM   #11
E2 Electrician
stickboy1375's Avatar
Rewards Points: 2,970
Yes.
Yes.
Yes.
Well, that was an easy one.
Old 08-01-2012, 05:00 PM   #12
E2 Electrician
Okay, lets duke it out, what code section would you call?
Old 08-01-2012, 05:05 PM   #13
E2 Electrician
This is only if you are running on the BOTTOM of joist.... we are talking about the sill plate and rim board.
Old 08-01-2012, 05:06 PM   #14
E2 Electrician
And the wires would not be in the way... they would be stapled on a sill plate or rim board.
Old 08-01-2012, 05:13 PM   #15
E2 Electrician
These are wires stapled to a sill plate... this is not a violation, As they are NOT stapled to the bottom of a joist.
Adding ground in old home ChaosTheory Electrical 6 06-16-2010 05:02 PM
Wire question RedBear Electrical 7 01-10-2010 06:28 PM
Running Under ground wire Robbro137 Electrical 1 08-21-2009 06:11 PM
running wire underground for outdoor outlet ponch37300 Electrical 11 06-26-2009 10:41 AM
old wire, backfed switch question Jack A. Trades Electrical 6 07-03-2008 12:05 PM