i am about to run wire for a 50A subpanel in a detached shed. i will have a circuit to connect to once i convert from an electric to a gas stove. but i first want to run the wire. i have about 30 ft of conduit buried already from the basement to the shed.
Q1: do i just need to run 3 exterior grade gauge 6 wires and can the ground wire be the same (insulated) as the hot and neutral ?
Q2: when setting the subpanel, does the ground bus connect to the ground wire coming in, in addition to the grounding rod, which i have driven into the ground about a foot away from the shed?
jbfan 03-15-2011 05:44 PM
Q1- The ground wire can be smaller, a #10 would work here.
Q2-The ground from the house and the rod connect to the ground bus in the garage.
You are going to run 4 wires to the garage right?
amakarevic 03-16-2011 12:37 AM
what's the 4th wire for ?
SD515 03-16-2011 06:29 AM
4 wires are used to install a sub-panel. 2 hots, 1 neutral & 1 ground. If you're installing a sub-panel in an outbuilding, you might as well take full advantage of its capabilities.
J. V. 03-16-2011 11:56 AM
Its the grounding conductor (EGC) and is required. It connects to the panel ground bar and to the rod. You need a disconnect out there too. 60 amp is the smallest you can go. The feeder can be 50 amp though.
amakarevic 03-16-2011 03:27 PM
so the 2 hots and the neutral should be gauge 6 and the ground can be smaller (gauge 10). does it matter if the ground is insulated?
jbfan 03-16-2011 03:37 PM
No, but it will be an easier pull with an insulated wire.
LyonsElecSupply 03-17-2011 12:23 AM
For future reference, I thought all wire inside conduit had to be insulated.....
amakarevic 03-17-2011 01:29 PM
hey y'all, please check out my new inquiry:
http://www.diychatroom.com/f18/thhn-...93/#post611347
much appreciated :thumbsup:
Jackofall1 03-17-2011 01:42 PM
Did and answered
Saturday Cowboy 03-17-2011 06:04 PM
This I have not heard. I agree that it almost always would be a good idea, but where a code reference for that statement? I am not sure but I believe that a bare ground is ok in pipe?