Help? Planning on using 2-2-4 Alum URD. Any ideas how this will work? Have 200 amp panel in house Using 100watt Breaker panel in shop. Will have a3volt drop. Will use a 100 amp breaker in the house panel. The 3 wire is sold at the big box stores.If the4 wire should be used , i will hunt it down. Thanks for the help
kola is offline   Reply With Quote
Old 06-04-2008, 10:38 PM   #2
Licensed Pro
Two things: You need 2-2-2-4 Al, and you need to protect at 90A at the main panel.
Old 06-05-2008, 04:15 PM   #3
Rewards Points: 82
And separate neutrals and grounds in the new sub panel. You also need a breaker in the sub panel. One inside at the main panel and one in the sub panel. Househelper is correct about needing four wires for the sub panel feeder. 2 Hots - 1 Neutral - and 1 ground (EGC).
Breakers are not rated in watts typically. You need to look for the amp (current) rating on the breaker in the shop.
What is the sub panel rated at in amps? If it is 60 amp (example) you use a 60 amp or less in the sub, even though you have a 90 amp breaker protecting the feeder.
Good luck.
Old 06-05-2008, 07:09 PM   #4
Cow
Originally Posted by HouseHelper View Post
You need 2-2-2-4 Al.
Shouldn't you be asking him if he's under the 08 code before you tell him he needs 4 wires?
Cow is offline   Reply With Quote
Old 06-05-2008, 11:21 PM   #5
Licensed Pro
No, 'cause I will always tell someone they need 4 wires for a subpanel, detached structure or not.
And Kola, remember you need to sink a ground rod or two at the shop also.
Old 06-06-2008, 10:13 AM   #6
Licensed Electrician
jrclen's Avatar
Rewards Points: 514
I'd like to add that although you will need to use a 90 amp breaker in the main panel to protect your new feeder, it will be fine to use a 100 amp main breaker panel in the shop.
John
jrclen is offline   Reply With Quote
Advice on basement shop wiring WoodworkerDave Electrical 4 04-05-2008 01:12 PM
Running new 2nd floor wiring on *exterior* of our home? drh Electrical 12 02-16-2008 07:27 PM
Running New Wiring to Attic PCC Electrical 12 02-08-2008 05:09 PM
Wiring New Shop, OK? woodman51jfk Electrical 18 12-17-2007 12:36 AM
Underground Wiring millipede Electrical 4 11-24-2006 11:00 PM