I'm adding an outside receptacle to the front of my house and will tap into it to run 120v underground about twenty feet to a weatherproof box. This will be a new 20a circuit. I think I have everything all set with the underground cable that will pass under a concrete walkway (cable in EMT, trench 18" below grade, etc.), except for a question about cable depth near footings. I want to have the 120v box butted up against a block wall, but because of the footing that sticks out 5" from the wall, I can't.
As far as I understand, I must have the cable at 18" until it comes up to the surface. With keeping within code (California), how can I go about getting the box against the wall with the footing in the way? Thanks.
blue sky is offline   Reply With Quote
Old 09-26-2011, 12:55 PM   #2
Electrical Contractor
jbfan's Avatar
Rewards Points: 654
Why are you using emt underground?
Are you running conduit all the way to the wall, or just under the walkway?
The cable needs to be protected where come out of the ground, you you can offset the conduit around the footings to get the box to the wall.
You are using uf cable, right?
jbfan is online now   Reply With Quote
Old 09-26-2011, 01:07 PM   #3
jbfan - I thought emt was required for underground, is pvc the better choice? Since the trench is only 18", I'm running conduit all the way to the wall. It sounds like I can put some elbows on the conduit to shape it around the footing to get the box close...that'll solve my problem. I haven't got the cable yet, but I was going to find out the correct cable for this...are you saying uf is what I need?
Old 09-26-2011, 01:14 PM   #4
jbfan's Avatar
Rewards Points: 654
Are you running conduit from the panel to the outside box?
If you run conduit all the way, you can use single wires, #12 thwn, black white and green.
An underground conduit is considered a wet location, and nm-b is not rated for a wet location, but uf is.
You can find some preformed 45's also.
Old 09-26-2011, 01:26 PM   #5
Yes, the sub-panel (not installed yet) will be on the other side of the wall (garage) and I will surface mount the cable on the garage interior. Since this circuit will power two receptacles, plus the underground fed outside box, would it be best to run nm-b to the two receptacles (above ground), then uf once the underground conduit begins?
Old 09-26-2011, 01:41 PM   #6
jbfan's Avatar
Rewards Points: 654
Without seeing your set-up, I would run nmb to each inside receptacle, and from the last one run mnb to and outside junction box.
Connect the pvc, and run single wires to the outside receptacle.
The pull will be much easier then cable.
Old 09-26-2011, 01:49 PM   #7
That sounds easy enough. So since pvc is good for this under gound job, when would someone use emt?
Old 09-26-2011, 02:03 PM   #8
jbfan's Avatar
Rewards Points: 654
Inside.
Old 09-26-2011, 03:25 PM   #9
Thanks for your help?
Old 09-28-2011, 02:16 PM   #10
Here's a couple follow up questions. Under the concrete walkway, there is a 6" pvc pipe that drains water to the front of the house and it is the same 18" depth as my conduit trench. To go around it means digging a lot more trench. Is it an issue to run the conduit directly on top of the 6" pvc drain? Also, do I need to glue the pvc conduit that holds the THHN? Or does it not matter?
Old 09-28-2011, 02:40 PM   #11
jbfan's Avatar
Rewards Points: 654
Run it on top of the drain, and glue the pipe.
Old 12-31-2011, 01:35 PM   #12
underground electrical feed
I want to have an RV electrical outlet about 16ft from my house. I plan to install a single 30A/120V recepticle on a post at that location. The feed will start from my main house panel. I understand I need to bury the sched 40 PCV 18" underground.
My problem is I have a walkway in-between that is about 2ft from the house. The walkway has a large PVC pipe underneath for cable runs but it is only about 8" below grade. How should I trench from the house to the sidewalk (2ft run) and from the other side of the side-walk to the post (10ft) ?
I will probably hire an electrician to do the wiring but want to prepare the site beforehand myself.
Thanks,
Brian
Bptsj is offline   Reply With Quote
What size wire to use running underground ms66cadillac Electrical 21 01-13-2011 11:14 AM
running outdoor cable from house to detached shed above ground amakarevic Electrical 2 11-19-2010 02:16 PM
Retaining Wall and Muddy Yard rjschwar Landscaping & Lawn Care 10 02-24-2010 12:55 PM
Underground Cable Question Livewire78 Electrical 7 12-09-2009 12:15 PM
running wire underground for outdoor outlet ponch37300 Electrical 11 06-26-2009 09:41 AM