Running Subpanel Supply Along Shed Ridge Beam - Electrical - DIY Chatroom Home Improvement Forum
Old 07-06-2011, 04:22 PM   #1
Rewards Points: 1,062
Question
running subpanel supply along shed ridge beam
i was wondering if there are any issues with running a 6/3 indoor cable supplying power to a 50A subpanel in a shed along the bottom of its 2x8 ridge beam. please see the attached diagram. the conduit with outdoor loose wires enters through the ground in the bottom left corner, then goes up to the JB where it connects to 6/3 indoor cable, which then travels to the front of the shed into the subpanel. i was gonna put the subpanel right above where it enters in the lower left but i also have a frost hydrant there which obstructs the space.
thanks
Old 07-06-2011, 05:38 PM   #2
Master Electrician
Rewards Points: 3,678
That's sure one small shed.
brric is offline   Reply With Quote
Old 07-06-2011, 05:40 PM   #3
Electrician
SD515's Avatar
Rewards Points: 504
Not really any issue if it’s not subject to physical damage, but it may be difficult to properly retain it with straps or staples if it’s on the 2” edge. May have to add a running board for the cable to have a better base to ride on. Can you run it down the 8” side?
Kyle
The Following User Says Thank You to SD515 For This Useful Post:
amakarevic (07-06-2011)
Old 07-06-2011, 05:41 PM   #4
Electrician
SD515's Avatar
Rewards Points: 504
But it's got 240V/50A's....and 5-400W low bays....Ken & Barbie are all set !!
Kyle
Old 07-06-2011, 05:42 PM   #5
Master Electrician
If this is the same installation as from your previous posts all you need to do is offset your panel slightly from the hydrant. You are way over engineering this.
Old 07-06-2011, 06:25 PM   #6
the problem is access to walls as i plan to have most wall space covered with shelving. next to the door is one of the few spaces i will have open, in addition to where the utility dock is where they come into the shed (lower left).
and yes, i think i can run it along the 8 side of the beam.
but thanks y'all
Old 07-06-2011, 06:37 PM   #7
Electrician
SD515's Avatar
Rewards Points: 504
Run it the best way to keep it protected.
Kyle
Old 07-09-2011, 05:01 PM   #8
Question
from the JB where this cable meets with THHN loose wires coming from the conduit underground, to the subpanel, i plan to run 6/3 NM loose without conduit, as though it was behind drywall. it would be exposed as the framing is exposed. i was wondering if this is permitted as i've noticed that cable usually runs in conduit where it doesn't run behind drywall, i.e. don't get to see much exposed NM cable.
Old 04-24-2016, 06:10 PM   #9
Rewards Points: 44
Re: running subpanel supply along shed ridge beam
I have a similar situation on a cathedral ceiling. I need to supply power to a ceiling fan and the most practical is running the cable under the ridge beam. The 2x12 rafters have metal joist hangers which I will have to otherwise snake around (x6). I suppose the other option is running it through the low end of the rafters which I may very well do but thought I would check on this first.
kurtp2 is online now   Reply With Quote
Moving ridge beam post brick_layer Carpentry 10 05-18-2011 11:43 PM