Old 06-27-2010, 01:09 PM   #1
Running new(up to code) ground wire & protection.
I recently replaced my old FPE breaker with a newer updated one simply due to the additional circuits I would be adding to the house (namely solar panels), under the instruction of a friend of a friend who's an electrician, he told me because I replaced it (and it's an obvious replacement) the ground needs to be brought up to code unless I want it to be flagged by the inspector.
Currently it's a 100amp panel, and the current ground consisted of a #6 wire being strung up to and attached to a cold water pipe that's somewhat close to the panel (maybe 10 feet), I was told that I need to connect a ground within 5 feet of where the cold water enters the ground, as well as connect to the house size of the gas lines as well (I don't get it, but whatever), and the wire needs to be at least #4 which I have plenty of (also need to hammer ground rods for a 2nd.. but whatever for now).
Since he left for vacation I can't get ahold of him however I'm wondering what sort of protection needs to be done for the ground wire as the cold is on the other side of the garage. Do I need to run the single wire in conduit? or can I drill through the studs (ala romex) and run the wire through there (even though it's not romex #4) or can the wire be exposed (stapled) because it's not carrying a load?
Thanks.
MikeSF is offline   Reply With Quote
Old 06-27-2010, 02:28 PM   #2
Totally screwed together
They sell ground wire at the big boxes already wrapped in flexible aluminumn sheathing, in 25' and 100' lenths. You need to have a continuous connection (no breaks) between your panel and your ground.
Your cold water pip isn't a true ground, but keep that connection as it does need to be bonded to. A pair of ground rods will be your true ground.
xxPaulCPxx is offline   Reply With Quote
Old 06-27-2010, 03:48 PM   #3
Master Electrician
You do not need sheathing on the ground wire to the water line. The water pipe ground is far superior to any two grounding rods- but you should do both.
brric is offline   Reply With Quote
Old 06-27-2010, 05:08 PM   #4
Licensed Electrical Cont.
Speedy Petey's Avatar
Agree.
Old 06-27-2010, 05:31 PM   #5
Thanks for the reply.
So just to make things clear, ground only needs to be stapled to the rafters to get to the water pipe? (unfinished basement area).
And yeah, I know two ground rods are additional, and thanks to San Francisco code is a necessity.
Old 06-27-2010, 05:44 PM   #6
Master Electrician
There are no rafters in a basement. You would be better off drilling the floor joists to accomodate the wire.
Old 06-27-2010, 06:38 PM   #7
nap
You talking to me?
nap's Avatar
If the water pipe is your only grounding electrode, any place the follows the NEC requires at least 1 rod in addition to the water pipe BUT in addition to the rod itself, the rod must show less than 25 ohms resistance to Earth or a 2nd rod must be installed so unless a person wants to go to the trouble of a resistance test, everybody just drives 2 rods in addition to the water pipe.
so, most of the country would require 2 rods, not just San Francisco.
Old 06-27-2010, 08:56 PM   #8
That is correct. Though carrying no current, they should still be treated like romex in that you protect the cable and keep it from been worn away by abrasion. That's less a concern with a single strand of thick copper, but is a concern with thinner stranded type that is much easier to handle and pull.
Old 06-27-2010, 09:23 PM   #9
Licensed electrician
Originally Posted by xxPaulCPxx View Post
Your cold water pipe isn't a true ground, but keep that connection as it does need to be bonded to. A pair of ground rods will be your true ground.
The water line ground is the primary. The rods would be the supplemental ground.
Old 06-28-2010, 11:44 AM   #10
It is primary as it is a better ground, with more surface area and longer contact surface than a 5/8" rod... until your water company comes out and replaces it with plastic pipe.
Oops! Hope no one gets the impression that it's OK to just ground off your water pipe. Right about now is when alot of the post WWII baby boom housing is getting their copper pipe replaced due to corrosion from soil contact under the slabs.
Old 06-28-2010, 12:18 PM   #11
Master Electrician
Why don't you explain to us how effective you think a pair of rods is for grounding?
Old 06-28-2010, 12:51 PM   #12
Compared to what?
A disconnected cold water pipe? A UFER? 3 or more Ground rods? Ground rods driven at a 45 degree angle? Ground plate?
Old 06-28-2010, 01:24 PM   #13
Master Electrician
Two standard 5/8" x 8' galvanized ground rods.
Old 06-28-2010, 02:03 PM   #14
Compared to what?
You want me to compare what I suggested to what I suggested?
Old 06-28-2010, 02:23 PM   #15
Going backwards in the posts, this might be why Brric is asking about the ground rods and their function.
running wire underground for outdoor outlet ponch37300 Electrical 11 06-26-2009 10:41 AM
hooking up dryer....bronx ny code SURFBUG Appliances 6 10-14-2008 10:41 PM
Grounding conduit instead of using a ground wire? stringtheories Electrical 10 08-02-2008 01:42 PM
Hot Tub Install--Grounding Rod Question statgeek_rob Electrical 16 09-15-2007 03:59 AM