Running electrical to a out building
I would run three (changed to) #2 copper or #O aluminum (red or black, black, white) and one #8 copper (green for ground). Use wet location wireing e.g. THWN in conduit buried 18 inches deep.
Alternative, #2-3 (O-3 aluminum) with ground copper direct burial Romex type cable buried 24 inches deep.
Put a double wide 240 volt 100 amp branch circuit breaker in the shop panel to connect the outbuilding feed to. Have a 100 amp (or greater) 120/240 volt breaker box as a subpanel (neutrals and grounds on separater terminal strips) in the outbuilding.
Either the subpanel in the outbuilding needs a master disconnect switch or breaker up top for the incoming feed or you need a separate box next to it with heavy duty (here 100 amp) double pole switch for a master disconnect. This is in addition to the (100 amp) breaker unit in the shop building panel.
Run a #6 copper wire from the outbuilding subpanel ground bus (terminal strip) to a pair of 8' ground rods at least 6 feet apart.
The disadvantages of crab apple trees. In summer, the apples are too sour to pick and eat. In winter the birds come and leave dropping all over the place.