Old 08-18-2007, 12:22 PM   #1
Rewards Points: 14
Running electric to a shed
I am looking to run an electric line to my shed I just built. I already have a subpanel at my hottub with two open spots for a breaker on it, so I plan to tap into that. It's about a 75 foot run to the shed. I plan to dig a trench and put the line in PVC. I don't want to use the underground cable because it's more expensive and you have to dig deeper. My question is whether you can use regular old 12/2 romex inside of the pvc that will be underground? I know most of the time you use stranded cable inside the pvc, but I already have some romex leftover and the stranded seems to be more expensive. Any help it appreciated. Thanks
msajeep is offline   Reply With Quote
Old 08-18-2007, 09:53 PM   #2
remodeling pro
It is best IMO not to use the UF cable, whatever your reason. I cannot understand how it is even allowed to bury ac voltage wire unprotected. Step up to 1" conduit, and I would invest in a coil of #10 instead of the #12 you already have. The larger wire will offer an ample supply line for any future modest power demand you may want from in the garage (power tools, landscape lighting, small above ground pool pump. It is easier and cheaper to have a larger wire than you need, than to have to resupply later. As you assemble the conduit, give a squirt of wire pulling lubricant into the end of one pipe at each joint, being sure to keep it off of the gluing area. I do not know of any code that prohibits "Romex" in this application, but I'm sure some electricians will reply if so.
troubleseeker is offline   Reply With Quote
Old 08-19-2007, 07:41 PM   #3
Licensed Pro
Wiring underground is considered a wet location, so you must use THWN single conductor wires or UF cable. If all you want is one circuit, three runs of #12 THWN (hot, neutral, ground) in 1/2" PVC will suffice. You will need a disconnect at the shed, but this can be a simple snap switch. I would use a GFCI breaker at the subpanel, but you could also use GFCI receptacles at the shed.
Old 08-19-2007, 08:23 PM   #4
remodeling pro
Glad to see your clarification on that. I did not know that single conductor wires were required in this situation. Curious.. do you know why ?, it seems that the extra jacket on the "romex" would be beneficial.
How about Uf cable in the conduit? also a no no?
Old 08-19-2007, 08:44 PM   #5
Agent 000
SecretSquirrel's Avatar
No one has mentioned the minimum burial depth for conduit. I'm going on memory but I *think* it's 18". Someone chime in if it's different.
SecretSquirrel is offline   Reply With Quote
Old 08-19-2007, 09:03 PM   #6
UAW SKILLED TRADES
Stubbie's Avatar
Rewards Points: 2,652
If the circuit is gfci protected before it goes outside and is 20 amps or less it can be buried at 12". Otherwise you are correct for most residential applications using pvc.
Stubbie
Old 08-19-2007, 09:21 PM   #7
UAW SKILLED TRADES
Stubbie's Avatar
Romex (NM-b) is not allowed underground or anywhere in a classified wet location. It can be ran in conduit but not underground or outside in a wet environment. The jacket is no help if the conduit floods.... it is not rated to be wet. The wires inside are rated thhn not th"w"n... w=wet. In a nutshell you must be in a dry location indoors to use romex.
UF can be ran in conduit underground ,however why do it? It is more expensive than individual conductors. So direct bury it that is what they make it for.
Stubbie
Old 08-19-2007, 09:53 PM   #8
remodeling pro
Stubbie
Was just curious about the UF in conduit, agreed it makes no sense to pay the extra cost for it to put it in pipe. Can't change my mind though about never allowing direct burial on any of our jobs. Conduit is plenty cheap enough as far as I'm concerned.
Old 08-19-2007, 10:40 PM   #9
Rewards Points: 14
Thanks for the info, although I'm still a little confused as to whether I can tie into my subpanel for the hot tub. Basically I have 6 gauge wire running form a subpanel in the house that goes to a 3 breaker subpanel outside my house. In this subpanel(which is mounted on the side of my house by the hot tub) I have a GFI breaker which is wired and that goes to the hot tub but there are also 2 other empty spots for additional breakers. Why woudl they put two more open spots in the subpanel if you couldn't use them?? Any help is appreicated
Old 08-20-2007, 10:40 PM   #10
UAW SKILLED TRADES
Stubbie's Avatar
I can't find anything that says you can't do as planned. It's a funny coincidence but I am doing a very similar installation early next week. I've spent a few days making dang sure I can use the spa panel. Looks like you have no problems using the spa panel nor do I.
Stubbie
Old 08-22-2007, 08:49 PM   #11
Is your #6 al is assume? Also what size ocpd do you have the wire on?
wooderson is offline   Reply With Quote
Old 04-12-2011, 02:24 PM   #12
18'' is correct for running pvc underground
WireNutter512 is offline   Reply With Quote
Old 04-12-2011, 03:33 PM   #13
Code will allow you to go as shallow as 6" (instead of 18") but then you need to cover with concrete....
duckdown is offline   Reply With Quote
Old 04-12-2011, 10:34 PM   #14
Rewards Points: 1,016
Summary:
  • single 120v 20a circuit
  • GFCI at the spa subpanel end
  • three runs of #12 THWN (hot, neutral, ground)
  • in 1" conduit, buried 12"
  • some kind of a disconnect at the out-building
Disagreements?
Old 04-12-2011, 11:53 PM   #15
Scared Electrician
Saturday Cowboy's Avatar
I can't see why you wouldn't go 120/240v, what do you plan on using?
Ragged Trousered Philanthropist
Please follow the code - its there for your safety no matter how inconvenient.
Saturday Cowboy is offline   Reply With Quote
HELP! Electric furnace won't stop running! knchat HVAC 3 12-28-2011 08:38 AM
Freedom 90 furnance not running reliably from generator jrielsky HVAC 6 02-12-2008 01:48 PM
Convert from electric heat to oil/propane? Badfish740 HVAC 7 05-15-2007 11:17 AM
Subpanel to Shed - Check my plan NateHanson Electrical 9 04-26-2007 09:56 PM
Venting a shed roof with 2/12 slope atulc Roofing/Siding 5 08-25-2006 07:28 AM