Uncle Mike 09-28-2011 03:04 PM
i currently have 220V line run from the main electric panel of the house to the front of the dock with #6 - 4 wires (about a 150 foot run). i need to run another 100 feet to the end of the dock for the new lift and the contractor only needs #10 wires. I don't think i can splice into the smaller wire, but wondered if i should i install a subpanel with cuttoff at the front of the dock and then run the #10 from there to the end?
mpoulton 09-28-2011 04:21 PM
Yes, that's a good solution. You can connect the #6 directly to the #10, as long as the breaker on the circuit is 30A or less. You may want to consider using #8 or #6 all the way down the dock since voltage drop is likely to be an issue on such a long run. A subpanel at the dock would be a good idea anyway, though, because you may want to add other loads like lights and receptacles later.