Old 08-25-2007, 07:43 PM   #1
running 14-2 romex
does anyone know how many runs of 14-2 you can put in a 1" hole in a stud ? and can you increase the size of the hole to 1 1/2 " for more wires ?
tibbsy is offline   Reply With Quote
Old 08-25-2007, 08:06 PM   #2
Licensed Electrical Cont.
Speedy Petey's Avatar
running 14-2 romex
This is a contentious question, but the bottom line is four cables would never be a problem in a 1" hole.
You cannot go bigger than 1" in a 2x4. In fact if you do go with 1" keep the hole DEAD CENTER in the framing. You need to stay 1.25" from the edge of the framing.
7/8" is a better choice.
Old 08-25-2007, 08:23 PM   #3
Electrician
running 14-2 romex
Pay attention to 334.80, where more than two NM cables containing two or more Current Carrying Conductors are bundled together and pass through wood framing that is to be fire- or draft-stopped, the allowable ampacity of each conductor shall be adjusted in accordance with Table 310.15(B)(2)(a).
chris75 is offline   Reply With Quote
Old 08-25-2007, 08:40 PM   #4
running 14-2 romex
Not wanting to get into the details of the code, or to get into the interpretation of 334.80, that is what I meant about it being a contentious issue.
A) As long as you stay under nine CCC's (current carrying conductors) there is NO issue with derating #14, #12, or #10. Ten or more CCC's derating becomes an issue.
Four 14/2's is eight CCC's.
B) Aside from the fire stop issue, not all AHJs consider running cables loosely through bored holes "bundling". In fact I see more that do not than do.
Old 08-25-2007, 09:34 PM   #5
Electrician
running 14-2 romex
I know it was a little too much info, but I still wanted it disclosed...
Freedom 90 furnance not running reliably from generator jrielsky HVAC 6 02-12-2008 02:48 PM
Running a generator for power outages tropic home Electrical 5 12-04-2006 09:22 PM
Running Romex up from basement to attic tra999 Electrical 1 07-25-2006 05:21 AM
Running Romex in the attic mdalli Electrical 7 07-06-2006 06:35 PM
Pulling romex thru wall with old romex? Doug Crf Electrical 4 04-11-2006 10:33 AM